Do i need to put a Symmetra LX 16kva UPS into bypass to change batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Do i need to put a Symmetra LX 16kva UPS into bypass to change batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

0 Likes
6
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

Do i need to put a Symmetra LX 16kva UPS into bypass to change batteries

Do i need to put a Symmetra LX 16kva UPS into bypass to change batteries while still running a full load?
After a power outage it has 4 failed batteries i want to reseat them before logging a support call, will i need to put the UPS into maintenance mode to do this?
Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

I was hoping to find an answer to a question I had within this discussion, but didn't. Will the Symmetra LX charge batteries while in Maintenance Bypass?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

You should be able to replace the batteries without going to bypass - all that will happen is that runtime will decrease if there's a power failure while you are replacing the batteries. If you go to bypass and there's a power failure, the connected equipment would lose power. Note that this is only true for batteries - if you remove a power module without going to bypass, the remaing power modules may not be sufficient to support the load, depending on the UPS configuration and load size.

I do want to caution you regarding simply removing / reinstalling the same battery module. The UPS will see this as a new battery module and assume it is in good working order. You won't discover that there is a fault with it until the next power failure or self-test/calibration run. This can give a false sense of security. Also, if you have several bad battery modules, I would check the serial numbers on all of the battery modukes to see if any of the others have similar date codes (the YY part of the xxYYxxxxxxxxx serial number). If they were all purchased at the same time, it is likely that the other battery modules are reaching the end of their useful service life as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

i agree with terry. it is not a good idea to reseat the battery modules. i'd contact tech support before you do that to avoid any problems and yes, in general, batteries are hot swappable. if no batteries are in the system or are not "good," the UPS is designed to go to bypass in that instance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:01 AM

Thanks for the input. All was running fine then the power went out and ran the unit dry, when the power came back on the unit started of as normal but started reporting 4 bad batteries. Batteries are only 3 years old and haven't really been used expect for this outage. They are reporting to have 9 min run time which is normal for the load. I will remove and reset them then run a self test and see what the state is after that, if they come up bad i'll buy new batteries. Any other suggestions?
Cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

no - that's fine but batteries like this do generally last for 3-5 years so depending on the location and environment, even if they have not gone through a lot of deep discharges, 3 years sounds normal to me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

Cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:12 AM . Last Modified: ‎2024-03-13 01:00 AM

I was hoping to find an answer to a question I had within this discussion, but didn't. Will the Symmetra LX charge batteries while in Maintenance Bypass?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore