My application requires that we be able to power down the entire rack using a single button mounted on the front (looks something like this: https://www.google.com/search?q=epo+switch&tbm=isch)
Do any of the APC Rack PDUs support connecting such an Emergency Power Off (EPO) switch, wired from a few feet away?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:00 AM . Last Modified: 2024-03-18 12:15 AM
They do not natively, only [most of] of the UPS models support it. Ideally, your Rack PDU would be connected to the output of a UPS so you'd do the EPO function there, upstream. Either way, you'd probably have to EPO whatever the Rack PDU is connected to for it's input or come up with a creative solution on somehow cutting the power to the PDU.
Let me know if you have further questions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:00 AM . Last Modified: 2024-03-18 12:15 AM
They do not natively, only [most of] of the UPS models support it. Ideally, your Rack PDU would be connected to the output of a UPS so you'd do the EPO function there, upstream. Either way, you'd probably have to EPO whatever the Rack PDU is connected to for it's input or come up with a creative solution on somehow cutting the power to the PDU.
Let me know if you have further questions.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.