Difference between an AP9635 and an AP9635CH?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Difference between an AP9635 and an AP9635CH?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

0 Likes
4
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

Difference between an AP9635 and an AP9635CH?

I recently came across an AP9635CH NMC2 management board with the Symmetra PX (sypx) application in place.  I've reflashed the firmware with the Smart-UPS app. I tested it with an older Smart-UPS and everything seems to be working fine.

APC's web site shows that the AP9635CH is discontinued, while the AP9635 is a current product. What if any difference is there in the two boards?

Edit for a possible feature request on the NMC2 boards (and maybe the NMC1, though I expect that one's time in the sun is through): for those of us using these boards in a "non commercial" environment, could there be an option added to remain logged on indefinitely? I realize most of the security implications from doing so, but this is a trade off I'm willing to make.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9635ch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

Hi William,

CH SKUs were initially intended for China only and had Schneider Electric branding on their front metal faceplate. This was the only difference - so no functional or firmware differences. Eventually, all NMCs began to be branded Schneider Electric so no need for the CH SKUs anymore.

On your feature request for NMC2, I can check into this but you can increase the timeout per user to 60 minutes now on 6.X.X firmware - is this still not adequate? For NMC1, I don't think we will make this change due to the card being pretty much discontinued and also because only one user can log in at a time and this is usually welcomed by most people to time sessions out if one is hung.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

Hi William,

CH SKUs were initially intended for China only and had Schneider Electric branding on their front metal faceplate. This was the only difference - so no functional or firmware differences. Eventually, all NMCs began to be branded Schneider Electric so no need for the CH SKUs anymore.

On your feature request for NMC2, I can check into this but you can increase the timeout per user to 60 minutes now on 6.X.X firmware - is this still not adequate? For NMC1, I don't think we will make this change due to the card being pretty much discontinued and also because only one user can log in at a time and this is usually welcomed by most people to time sessions out if one is hung.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

Thank you for the information. It might be an interesting story as to how this unit ended up in the US!

I was unaware that the login timeout could be increased to 60 minutes on the NMC2. (I only have two of them now.) I have changed that setting and will see if the result is acceptable. I'll frequently slap one of the more basic management cards into a UPS with fresh batteries to watch them charge from afar or (in the case of cards so equipped) to check on temperature and humidity probes in a remote area. It's quite handy on a sporadic basis just to refresh the page and see new data without having to log in again. (A better way might be to write a program that handles SNMP data and can display it, but I'm lazy and not terribly experienced with such.)

I've never actually had a session hang up on an NMC1, so perhaps I'm just lucky. cool

It'd be awesome if there was a way in which the NMC1 firmware could transition to some sort of community supported effort, but I would imagine that certain realities prevent that from becoming a reality.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

I often use GetIF -- it's free and can graph SNMP variables.

Mark, the forum regular with the UPS that fell off the empire state building, likes to monitor charge/discharge cycles by using Excel's "web query" feature with the data log. Excel periodically grabs the data keeping it logged in.

You could also embed the target page in an iframe and refresh it before autologout.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:39 AM . Last Modified: ‎2024-03-13 12:45 AM

Hi William,

You're welcome. The CH SKUs briefly were shipped in models globally that wanted the Schneider branding, like some 3 phase UPS units, prior to the standard SKUs being switched over to their Schneider branding - so it could've been in China at one point but likely not and was perhaps in a US unit somewhere that used the CH SKU briefly. laughing But we can pretend! Haha

I also think you're right on certain other realities preventing NMC1 from becoming a community effort.. people love these older cards though I understand! 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore