Did my Runtime Calibration complete properly?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Did my Runtime Calibration complete properly?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2022-06-29 04:06 PM

0 Likes
3
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-29 04:06 PM

Did my Runtime Calibration complete properly?

I have a Symmetra 80K and I ran a runtime calibration for the first time, perhaps ever.

 

In the event log I see:

Date Time User Event

 2022-06-2900:06:08DeviceUPS: Runtime no longer below selected threshold.
 2022-06-2823:49:05DeviceUPS: A low battery condition no longer exists.
 2022-06-2823:49:03DeviceUPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
 2022-06-2823:48:57DeviceUPS: Runtime calibration canceled.
 2022-06-2823:47:52DeviceUPS: Runtime below selected threshold.
 2022-06-2823:41:16DeviceUPS: Started a runtime calibration.
 2022-06-2812:25:17DeviceUPS: Passed a self-test.
 2022-06-2812:24:16DeviceUPS: Started a self-test.

 

Is this normal?

 

I'm asking specifically because I had done many self-tests in the past, and they always log a 'Started' and 'Passed' event to the log, which I included one of for reference above.

The Runtime Cal, though, logs a 'Start' event , and then a 'canceled'.  I would maybe expect it to say 'complete' or 'Passed', instead of canceled. 

 

The RED led was lit at the end of the cal too.  Though I suspect that was just because the runtime available was below alert threshold at the end of the cal which I did expect.

 

I was wondering if the low-runtime alert threshold causes a cal to 'cancel'.  But it's over a minute apart so I doubt it.

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2022-06-30 12:06 PM

0 Likes
2
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-30 12:06 PM

Hi,

 

You can find a FAQ document which discusses this topic here:

 

https://www.apc.com/us/en/faqs/FA156154/

 

I hope this helps!

 

PS the calibration will stop prematurely under certain conditions (i.e mains failure during the test). When low DC (or fuel <25%) is reached during the calibration it will mark the end of the test.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2022-07-06 10:24 PM

In response to al_buffington
0 Likes
1
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-06 10:24 PM

Thank you Al! your knowledge of these products is excellent!!!


I read FA156154 though and it explains an error in how the Gen 1 NMCs (AP9617, AP9618, AP9619) report calibration events.


The FA notes that it does not apply to AP9630, which is the NMC we have, Hardware Revision 05 running sy3p v7.0.4 on aos v7.0.4.

I'm very tempted to retry calibration again to duplicate the error. But I've also read that we should only do it once a year and the implication is it damages the remaining lifetime of the batteries.


On the diagnostic tests screen, I see:
Self-Test
Passed on June 29, 2022
Calibration
Not Available on June 28, 2022

In the NMC event log, I see:
Date Time User Event
2022-06-29 18:08:12 Device UPS: Passed a self-test.
2022-06-29 18:07:02 Device UPS: Started a self-test.
2022-06-29 00:06:08 Device UPS: Runtime no longer below selected threshold.
2022-06-28 23:49:05 Device UPS: A low battery condition no longer exists.
2022-06-28 23:49:03 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
2022-06-28 23:48:57 Device UPS: Runtime calibration canceled.
2022-06-28 23:47:52 Device UPS: Runtime below selected threshold.
2022-06-28 23:41:16 Device UPS: Started a runtime calibration.
2022-06-28 12:25:17 Device UPS: Passed a self-test.
2022-06-28 12:24:16 Device UPS: Started a self-test.
2022-06-28 06:10:11 Device UPS: Passed a self-test.
2022-06-28 06:08:59 Device UPS: Started a self-test.


I want the runtime displayed on the UPS to be as accurate as possible. So I'd like to know that runtime cal completed successfully. I reviewed the logs on the lcd display on the front of the symmetra and noted that simple self tests are logged as "On Batt" and then "Self Test Passed". The calibration was logged as: (In Order)

Runtime Cal Started

On Batt

Runtime Below Limit

Runtime Cal Stopped

Low-Battery

Online

Battery Recharged

Runtime Above Limit


The word "stopped" is what I'm not sure about... if it should say 'Passed' perhaps.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2022-07-07 06:42 AM

In response to ojfsdi
0 Likes
0
1118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-07 06:42 AM

Hi,

 

I've been working with the PX since its inception so I've picked up a few tidbits of knowledge over the years :). The calibration won't log a status of "passed" because it's not really a test that passes or fails. Its sole purpose  is to adjust the runtime on the front display. Its there because the UPS does not auto adjust the runtime based on battery performance during normal operation unless there is a deep discharge (100% to 25% capacity) of the batteries  (either though the calibration or an extended power outage). Based on the duration of the calibration you should be able to estimate the total runtime and compare it to what you see on the display. I suspect it will be pretty accurate. Hope this helps!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of