Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Could not connect to the vCenter Server over the network. PCNS 3.1 (VMWare vSphere connection issue)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Could not connect to the vCenter Server over the network. PCNS 3.1 (VMWare vSphere connection issue)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

0 Likes
3
2623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

Could not connect to the vCenter Server over the network. PCNS 3.1 (VMWare vSphere connection issue)

Hi,

I am stuck at this error when configuring the network shutdown client (pcns v3.1) for VMWare

When the client is installed the initial configuration wizard pops up in the webinterface, there we choose for "Host managed by vCenter Server." and fill in the vCenter Server IP Address/Hostname, vCenter Server Username and vCenter Server Password.

Our vSphere Server version is 5.1, and it is installed on a dedicated physical machine. (not part of the domain)

The PCNS 3.1 is installed on a vMA 5.5 and runs in our VMWare cluster.

I followed the APC application note #180 (at the end --> Active Directory / VMware Single Sign-On Configuration http://www.apcmedia.com/salestools/SJHN-92FLU8/SJHN-92FLU8_R0_EN.pdf)

but when we try connecting with one of the ESX Admins we still get the same error message.

We can perfectly logon with the domain account (ESX Admins) in the vSphere webinterface / vSphere client. So the Active Directory single sign on (SSO) seems to work properly.

I can't find any logging in the vMA where the client is installed.

I also tried disabling the windows firewall with no luck.

Both the vMA with the PCNS 3.1 and the vSphere Server are in the same subnet.

Anyone an idea where I can find additional error logs or a solution to this particular problem?

I was thinking to upgrade my vSphere Center to version 5.5 but I thought that it should work with the vSphere Center 5.1 also.

Regards

Stijn

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 3.1
  • center
  • network
  • pcns
  • powershute
  • shutdown
  • vmware
  • vsphere
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

0 Likes
0
2624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

Hello,

I googled the error message containing the SSL certificates and was able to fix the problem

Disable (hash out) the following line in

/opt/APC/PowerChute/jre1.7.0_45/lib/security/java.security

jdk.certpath.disabledAlgorithms=MD2, RSA keySize < 1024

Regards

Stijn

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

0 Likes
0
2624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

Hi,

You can enable debug logging by editing log4j.xml in the group1 directory. This will create a the error.log file in that directory.

Stop the PCNS daemon, edit log4j.xml as below, save it and re-start the daemon.

       

       

   

Change the above to:

       

       

   


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

0 Likes
0
2624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

Hi Bill,

Thanks for the support!

Now I know that the error is related to ssl certificates.

DEBUG 2138772592@qtp-1650487184-2 com.apcc.m11.components.WebServer.CfgWizard.pages.VCenterServerDetailsPage - Connection to vCenter Server could not be made

java.rmi.RemoteException: VI SDK invoke exception:javax.net.ssl.SSLHandshakeException: java.security.cert.CertificateException: Certificates does not conform to algorithm constraints

Somebody an idea how to solve this?

Kind regards,

Stijn

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

0 Likes
0
2625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:05 AM . Last Modified: ‎2024-03-05 01:47 AM

Hello,

I googled the error message containing the SSL certificates and was able to fix the problem

Disable (hash out) the following line in

/opt/APC/PowerChute/jre1.7.0_45/lib/security/java.security

jdk.certpath.disabledAlgorithms=MD2, RSA keySize < 1024

Regards

Stijn

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore