Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Connecting multiple SMX3000LV UPS
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0106:00 AM. Last Modified: 2024-03-0512:01 AM
Connecting multiple SMX3000LV UPS
I would like to know if I can use the supplied USB connectors to connect to a server I have loaded Server, Console and Agent on. I would like to be able to monitor the UPS this way. Or, do I have to purchase the network module in order to have an IP as I don't see a way for the Powerchute Business Edition software to locate the two UPS without the IP...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0106:00 AM. Last Modified: 2024-03-0512:01 AM
Each installation of PowerChute Business Agent can only support one UPS for monitoring/graceful shutdown. You can install the PowerChute Business Edition Agent on two separate computers and connect one via USB to each UPS. Then, you can have the server and console components installed some place to monitor those two agents and gracefully shutdown each Agent independently.
You only need to pursue using the Network Management Card in each UPS if you are trying to set up a multiple UPS scenario in the sense of having servers with dual power supplies for redundancy and having each server only shutdown gracefully when both UPSs are on the verge of shutting down. If you do that, then you use PowerChute Network Shutdown software.
So I guess the answer is, it depends. Let me know if you need clarification.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0106:00 AM. Last Modified: 2024-03-0512:01 AM
Each installation of PowerChute Business Agent can only support one UPS for monitoring/graceful shutdown. You can install the PowerChute Business Edition Agent on two separate computers and connect one via USB to each UPS. Then, you can have the server and console components installed some place to monitor those two agents and gracefully shutdown each Agent independently.
You only need to pursue using the Network Management Card in each UPS if you are trying to set up a multiple UPS scenario in the sense of having servers with dual power supplies for redundancy and having each server only shutdown gracefully when both UPSs are on the verge of shutting down. If you do that, then you use PowerChute Network Shutdown software.
So I guess the answer is, it depends. Let me know if you need clarification.