Connecting a ups to a ups

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Connecting a ups to a ups
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
JamesGled
JamesGled
Cadet

Posted: ‎2025-04-04 02:02 PM

0 Likes
2
541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-04 02:02 PM

Connecting a ups to a ups

We have a small data centre with SRT300, these have two power supplies one connected to an AP4423 apc power switch which is connected to the rack power untis and the other connected to to a wall circuit which I have been advised is connected to a larger UPS. 

 

If there is a powercut will the bigger UPs 

 

If the rack mounted SRT300 battery has failed will the bigger UPS be able to keep the racks running.  On one hand I have read that it is not possible for the bigger UPS to move power to another UPS

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2025-04-07 11:40 PM

1 Like
0
491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-07 11:40 PM

Good Morning

 

From my understanding is that your ATS is supplied by two UPS systems. One in the rack, and the other via a bigger UPS via the wall circuit. For example If the small rack UPS is connected to the A source of the ATS and the Bigger UPS to the B source, Then the ATS will select the best source of power. If the small UPS fails the ATS will switch to the larger UPS. The larger UPS does not supply the smaller UPS, Unless its also fed from the same wall circuit. however with the larger UPS outside of your control, I would suggest testing to make sure that the wall circuit is fed from a UPS, and that the larger UPS is able to cope with the additional load. In addition if the larger UPS exists and is working.

Hope this helps

 

Best Regards

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Kirk Teken
Kirk

Posted: ‎2025-04-07 06:18 AM

1 Like
0
521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-07 06:18 AM

You’ll need to restate your question as it doesn’t make any sense. If I try to decipher what your asking than this leads to more questions for you to provide an answer to.

 

You also need to understand the basics of what the three devices are tasked to do.

 

1. I’ll start with the obvious one which is the AP4423 is a ATS (Automatic Transfer Switch). It’s only job is to transfer power to another input power source (B) if the primary input (Source A) has been lost.

 

2. Wall Outlet: I’m going to assume this wall outlet is a protected circuit. This typically in a real enterprise environment means that circuit is protected and powered by a back up (Generator). 

It’s not a UPS . . . 

3. SRT3000: If I take what you stated literally as to (IF) the SRT3000 failed. Everything connected to it like servers will either power down or lose power.

 

Obviously this is dependent upon the failure mode! If it’s a depleted battery cartridge the system will resume (if programmed) upon AC restore.

 

If the UPS has failed internally all the connected loads will not resume upon AC restore.

 

As to your question as to (IF) the wall outlet can handle the load only testing and validation can determine this! ☝️

 

Lastly, do not mistake a ATS vs a Maintenance Bypass Switch as the same!

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2025-04-07 11:40 PM

1 Like
0
492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-07 11:40 PM

Good Morning

 

From my understanding is that your ATS is supplied by two UPS systems. One in the rack, and the other via a bigger UPS via the wall circuit. For example If the small rack UPS is connected to the A source of the ATS and the Bigger UPS to the B source, Then the ATS will select the best source of power. If the small UPS fails the ATS will switch to the larger UPS. The larger UPS does not supply the smaller UPS, Unless its also fed from the same wall circuit. however with the larger UPS outside of your control, I would suggest testing to make sure that the wall circuit is fed from a UPS, and that the larger UPS is able to cope with the additional load. In addition if the larger UPS exists and is working.

Hope this helps

 

Best Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore