Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:20 AM . Last Modified: 2024-02-14 02:36 AM
Hello
Dears i'm facing this problem since today morning ! one of the A.Cs shows me alarm that is Compressor high Pressure Alarm>
so kindly guide me what should do ?
AC model is = ACRP102
ISX Central
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:21 AM . Last Modified: 2024-01-31 02:56 AM
Hello Altaleb.
The high head pressure alarm indicates a possible issue with the condenser. Check that there are no blown breakers for the condensing unit (outside unit) and that the fans are spinning. If this alarm has only happened once, reset the alarm on the unit and monitor it closely. If the alarm keeps happening or comes back, please call your local tech support for further troubleshooting to identify the exact issue.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:21 AM . Last Modified: 2024-01-31 02:56 AM
Hello Altaleb.
The high head pressure alarm indicates a possible issue with the condenser. Check that there are no blown breakers for the condensing unit (outside unit) and that the fans are spinning. If this alarm has only happened once, reset the alarm on the unit and monitor it closely. If the alarm keeps happening or comes back, please call your local tech support for further troubleshooting to identify the exact issue.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:21 AM . Last Modified: 2024-02-14 02:36 AM
thank you for your great support
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.