Communication has been lost to the ATS controller!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Communication has been lost to the ATS controller!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
becir
becir
Cadet

Posted: ‎2023-01-09 12:20 AM

0 Likes
5
3852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-09 12:20 AM

Communication has been lost to the ATS controller!

Hi all

 

I have a problem with an AP9538. I update the ATS Network Card Firmware to v7.0.4. 

The Update finished successful but since then the ATS Controller is not reachable. 

On the Login Page it says "Communication has been lost to the ATS controller!"

I tried to reboot the Controller without luck. Any suggestions what could resolve the issue?

 

Regards

Becir

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
JonPro
Commander JonPro Commander
Commander

Posted: ‎2023-01-10 04:22 PM

0 Likes
1
3837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-10 04:22 PM

Hi @beic

 

I am sorry to hear about the issue that you are experiencing with the ATS.  If there is a communication lost issue with the ATS, it is a possible hardware issue.  To start with, let's do a firmware recovery and format the card by following the FAQ article below.

 

Also, can you DM me your email address and I will send you the ATS4G v7.0.4 firmware.

 

Video: How do I upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device ... 

 

Video: Using Network Management Card 2 (NMC2) bootmonitor to recover/upgrade firmware - FA293874 

Reply

Link copied. Please paste this link to share this article on your social media post.

becir
becir
Cadet

Posted: ‎2023-01-15 10:50 PM

In response to JonPro
1 Like
0
3815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-15 10:50 PM

Hi JonPro

 

Thanks for your reply. I tried the firmware recovery without luck. I'm looking for a Serial to USB Converter and will try to format the card. 

 

Regards

Becir

Reply

Link copied. Please paste this link to share this article on your social media post.

33
Crewman 33
Crewman

Posted: ‎2024-03-05 08:31 AM

0 Likes
1
3119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-05 08:31 AM

Hi all.

I have same issue with APC AP4424, NMC AP9538.

"Communication Status - Communication has been lost to the ATS controller!"
It start after firmware upgrade and reboot, from "apc_hw05_aos656_ats4g656_bootmon108" to "apc_hw05_aos712_ats4g712_bootmon109".
I also try flash NMC from "bootmon" several times, but no changes.
No warranty, seal is broken, ATS removed from AC power and i can open it.
Can send you some instructions on checking something under the lid?
Attachments
  • Tags:
  • AP4424
Reply

Link copied. Please paste this link to share this article on your social media post.

33
Crewman 33
Crewman

Posted: ‎2024-03-06 07:45 AM

0 Likes
0
3090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-06 07:45 AM

Hi all.

Today update.

I connect NMC to different ATS same model, communication to ATS controller correct and receive data.

It seems that the 'ATS controller' module is fault. Is it possible to check it without contact technical support?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-03-06 11:40 AM

In response to 33
0 Likes
0
3108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-06 11:40 AM

APC will not provide you a wiring schematic much less reply to your question as to how to diagnose the internal electronics. 🤦‍♂️

 

As it relates to upgrading any firmware on a APC product. It’s highly recommended that a person do so only while guided by a (live) APC Technical Support personnel over the phone!

 

Firmware should only be loaded to address a bug, security, or to obtain enhanced features. That makes the product better to use or integrate.

 

As seen by your personal experience and thousands of others around the world. Upgrading firmware can and will brick a perfectly good working unit! 👎

 

NOTE: It’s imperative to note as it relates to the ATS. The secondary power source must be removed when firmware is loaded. This is because during the upgrade process it will cause the ATS to erratically transfer back and forth between primary & secondary outputs!

 

This action can and will burn out the internal relays of the ATS or cause carbon buildup on the relay contacts. As this condition happens it causes the ATS processor to declare a fault which results in a corrupted firmware upload / completion. 

Let us know how this all turns out good or bad. 👍🍺

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore