Translate to:
Please select
  • English (English)
  • French (Français)
  • German (Deutsch)
  • Indonesian (Bahasa Indonesia)
  • Italian (Italiano)
  • Portuguese (Português)
  • Russian (Русский)
  • Spanish (Español)
  • Thai (ไทย)
  • Turkish (Türkçe)
  • Vietnamese (Tiếng Việt)
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Cisco 4507E with 4200w power supply

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
Enter a search word
    Turn off suggestions

    Didn't find what you were looking for? Explore advanced search

    Enter a search word
      Turn off suggestions

      Didn't find what you were looking for? Explore advanced search

      Enter a user name or rank
        Turn off suggestions

        Didn't find what you were looking for? Explore advanced search

        Enter a search word
          Turn off suggestions

          Didn't find what you were looking for? Explore advanced search

          Enter a search word
            Turn off suggestions

            Didn't find what you were looking for? Explore advanced search

            cancel
            Turn on suggestions
            Showing results for 
            Show  only  | Search instead for 
            Did you mean: 
            Important Note
            • Home
            • Schneider Electric Community
            • APC UPS, Critical Power, Cooling and Racks
            • APC UPS Data Center & Enterprise Solutions Forum
            • Cisco 4507E with 4200w power supply
            Options
            • Mark Topic as New
            • Mark Topic as Read
            • Float this Topic for Current User
            • Bookmark
            • Subscribe
            • Mute
            • Printer Friendly Page
            Invite a Co-worker
            Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
            You have entered an invalid email address. Please re-enter the email address.
            This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
            Please enter email address
            Send Invite Cancel
            Invitation Sent
            Your invitation was sent.Thanks for sharing Exchange with your co-worker.
            Send New Invite Close
            Top Experts
            User Count
            BillP
            Administrator BillP Administrator
            5060
            voidstar_apc
            Janeway voidstar_apc
            196
            Teken
            Spock Teken
            136
            Erasmus_apc
            Sisko Erasmus_apc
            112
            View All

            Free

            English

            Data Center Certified Associate Exam Development Path

            Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

            4.0
            Register Browse SE University

            Invite a Colleague

            Found this content useful? Share it with a Colleague!

            Invite a Colleague Invite
            Solved Go to Solution
            Back to APC UPS Data Center & Enterprise Solutions Forum
            Start a Topic
            Solved
            Anonymous user
            Not applicable

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            0 Likes
            3
            1173
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            Cisco 4507E with 4200w power supply

            I have several closets with dual SmartUPS 3000 power supplies. I am planning to install Cisco Catalyst 4507E chassis using the 4200w power supplies. According to specification for this power supply
            (http://www.cisco.com/en/US/prod/collateral/switches/ps5718/ps4324/product_data_sheet09186a00801f3dd9...)
            To operate with needed amount of power to drive just data services (no POE) the following input is required:
            "Two 12A at 100 VAC"
            The APC SmartUPS 3000 a 120v UPS rated for "Max Configurable Power 2250 Watts / 3000 VA". The SmartUPS is plugged into utility power via L5-30.

            So the max VA the 4500 could drawn is 12 x 100 x 2 = 2400. Which I assume means plugging both AC inputs from the 4200w power supply into a SmartUPS 3000 should not exceed the capacity of the UPS under any power draw condition.

            Labels
            • Labels:
            • Smart-UPS & Symmetra LX | RM
            • Tags:
            • 4500
            • cisco
            • smartups
            Reply

            Link copied. Please paste this link to share this article on your social media post.

            • All forum topics
            • Previous Topic
            • Next Topic

            Accepted Solutions
            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            0 Likes
            0
            1173
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            hi,

            your calculations are correct. the only problem is - the output of the Smart UPS is 120v. if the device has a NEMA 5-15 plug, it will be fed 120v. i'd double check on the actual wattage draw of each of the power supplies to get a more accurate measure of what you need. i tried to find it on the page but maybe i missed it.

            See Answer In Context

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Replies 3
            Anonymous user
            Not applicable

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            0 Likes
            0
            1173
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            Well I assume if the voltage was higher that would mean the amps needed would be lower. But then again I am guessing at most of this stuff. So I assumed that if it was rated at 12amps at 100v but the supply was actually 120v that the required amps would be lower? I could of course be wildly off on this point.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            0 Likes
            0
            1173
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            yeah you are right essentially. as the voltage climbs higher, less amps are required and vice versa. i'd just make sure there isnt a problem with providing the equipment more voltage even though it equals the same amount of VA.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            0 Likes
            0
            1174
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM

            hi,

            your calculations are correct. the only problem is - the output of the Smart UPS is 120v. if the device has a NEMA 5-15 plug, it will be fed 120v. i'd double check on the actual wattage draw of each of the power supplies to get a more accurate measure of what you need. i tried to find it on the page but maybe i missed it.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Preview Exit Preview

            Photos

            • Upload Upload
            • URL URL
            • Saved Photos Saved Photos
            Upload location
            • Add Photos to Album:
            • New Album
            • Upload location
              • Add Photos to Album:
              • New Album
              Drag here to start uploading
              Drag photos here or
              Tap for upload options
              You must install or upgrade to the latest version of Adobe Flash Player before you can upload images.
            Photos

            never-displayed

            You must be signed in to add attachments

            never-displayed

             

            You’ve reached the end of your document

            WHAT’S NEXT?

            Ask our Experts

            Didn't find what you are looking for? Ask our experts!

            My Dashboard

            Check out the new Feeds and activities that are relevant to you.

            To The Top!

            Forums

            • APC UPS Data Center Backup Solutions
            • EcoStruxure IT
            • EcoStruxure Geo SCADA Expert
            • Metering & Power Quality
            • Schneider Electric Wiser

            Knowledge Center

            Events & webinars

            Ideas

            Blogs

            Get Started

            • Ask the Community
            • Community Guidelines
            • Community User Guide
            • How-To & Best Practice
            • Experts Leaderboard
            • Contact Support
            Brand-Logo
            Welcome to Schneider Electric Community!
            Forum-Icon

            You have two options to continue your visit.

            LOGIN / Register

            Why logging in?
            • You enable the complete set of features available, such as posting, sharing, subscribing, private messaging and more.
            • You unlock the access to the whole content that Schneider Electric Community has to offer, including the gated items and the special events.
            And it’s free of charge!!!

            OR

            Continue as a guest

            Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

            Welcome!

            Welcome to your new personalized space.

            of 1

            Explore
            Translating the page…
            The page is currently translating. Please wait.
            Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.