Changing passwords on InfrastruXure Manager and PDUs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Changing passwords on InfrastruXure Manager and PDUs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

0 Likes
3
3177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

Changing passwords on InfrastruXure Manager and PDUs

So, I wanted to change the passwords on my InfrastruXure Manager local admin user (apc), the Administrator Account (apc), the FTP Settings account (apc), and also the remote PDU Administrator user (apc).

When I change them, all the devices stop communicating to the InfrastruXure Manager, so I think I am missing a step.

I searched the documentation, and the forums and couldn't find anything really specific to my situation.

Anyone have any experience with this?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

0 Likes
0
3177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

Thanks for the quick reply.

I am not seeing those options you mentioned, I am rather new to this environment, so that may be it. But it also may be that we are running an older version of InfraStruXure Manager.

Im running on;
Version: 4.6.1 Build 23
Model Number: AP92200

What I am trying to do is move away from the default PW. Here is what I have done;

- From the manager window, System Management (pull down) - Authentication Settings - Configure Local Users - Click on "apc" user - Click Modify - Enter new password twice - Click "Ok" - Then click Apply once back at the Authentication Settings window.

- Then I go back into System Management (pull down) - Device Access - Administrator Accounts (tab) - Click on "apc" user - Click Modify - Enter new password twice - Click "Ok" - Then click Apply once back at the Device Access window.

- Then I go back into System Management (pull down) - Device Access - FTP Settings - Click on "apc" user - Click Remove - Click Add - Add "apc" user and the new password twice - Click "Ok" - Then click Apply once back at the Device Access window.

All of the above was done from within the InfraStruXure Manager window.

I then moved onto each device;

- Right click on the first "Metered Rack PDU" (model AP7862) - Select Device Details (this brings up the device window) - Click on the Administration tab - Under "Local Users" I am on "administrator" - Change password for "apc" user - click Apply.

I repeated the above for each of the Rack PDUs.

The result is the InfraStruXure Manager no longer talks to them. Looks like an authentication issue. When I right click on one of the Rack PDUs and open Device Details, it prompts me for a User/PW. If I enter the new PW it lets me in just fine. It seems like the Manager is some how holding onto the original PW, or I am missing a step in my process.

Any idea's?

Thank you!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

0 Likes
0
3177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

Figured it out.

It was the "HTTP Properties" user info I needed to update.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

0 Likes
0
3177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

There are a couple of other settings you might need to look at.

Central communicated with devices over SNMP.
Default community strings are "public" and "private". If these have been changed on the devices, the Central will lose connectivity with the device. Modify this under Device/Device Scan Settings.

If you have changed the login settings on the device, you will receive a login dialog when you launch to the device. To auto login set the Device Launch Settings in Central. Right click the Device/Device Launch Settings.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

0 Likes
0
3178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:09 AM . Last Modified: ‎2024-03-11 03:12 AM

Thanks for the quick reply.

I am not seeing those options you mentioned, I am rather new to this environment, so that may be it. But it also may be that we are running an older version of InfraStruXure Manager.

Im running on;
Version: 4.6.1 Build 23
Model Number: AP92200

What I am trying to do is move away from the default PW. Here is what I have done;

- From the manager window, System Management (pull down) - Authentication Settings - Configure Local Users - Click on "apc" user - Click Modify - Enter new password twice - Click "Ok" - Then click Apply once back at the Authentication Settings window.

- Then I go back into System Management (pull down) - Device Access - Administrator Accounts (tab) - Click on "apc" user - Click Modify - Enter new password twice - Click "Ok" - Then click Apply once back at the Device Access window.

- Then I go back into System Management (pull down) - Device Access - FTP Settings - Click on "apc" user - Click Remove - Click Add - Add "apc" user and the new password twice - Click "Ok" - Then click Apply once back at the Device Access window.

All of the above was done from within the InfraStruXure Manager window.

I then moved onto each device;

- Right click on the first "Metered Rack PDU" (model AP7862) - Select Device Details (this brings up the device window) - Click on the Administration tab - Under "Local Users" I am on "administrator" - Change password for "apc" user - click Apply.

I repeated the above for each of the Rack PDUs.

The result is the InfraStruXure Manager no longer talks to them. Looks like an authentication issue. When I right click on one of the Rack PDUs and open Device Details, it prompts me for a User/PW. If I enter the new PW it lets me in just fine. It seems like the Manager is some how holding onto the original PW, or I am missing a step in my process.

Any idea's?

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore