Challenges with AP9631 Event Action Settings

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Challenges with AP9631 Event Action Settings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
6
3175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

Challenges with AP9631 Event Action Settings

Hello,

I am trying to configure the Event Action settings for a UPS. I have three email addresses that need to receive alerts. One address is for critical events, another for warning events, and the last for informational events. I am configuring the event actions by groups. I can go through the steps via the web interface and receive the success statement after programming each one. However, after programming all three, when I go look at the config.ini file or call up any specific event, I see that it has does not save all of the changes. In fact, it seems to save updates to random event lines.

The general settings that I am trying to save are:

  • critical events
    • send to email address #2
    • 5 minute delay
    • 15 minute repeat interval
    • repeat until condition clears
  • warning events
    • send to email address #3
    • 5 minute delay
    • 30 minute repeat interval
    • repeat until condition clears
  • informational events
    • send to email address #4
    • 5 minute delay
    • 60 minute repeat interval
    • repeat until condition clears

The UPS is a SURTA2000XLRM2U with an AP9631 NMC.

The NMC is brand new from the box with factory applied FW Revisions:

  • apc_hw05_aos_517.bin
  • apc_hw05_sumx_517.bin
  • apc_hw05_bootmon102.bin

The goal is to get this UPS configured correctly, download the config.ini and then upload it to the other units at my company.

Any help would be greatly appreciated.


Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
0
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

I have a feeling this may be working but since it is confusing where to actually look to validate it, you're being a little mislead which isn't you're fault. (This is something we're working to clarify and make easier to understand in future firmware revisions).

Here is what you should do or how I would do this and let me know if by what I say, you've found a difference in steps or have further questions.

I might recommend you reset Event Action notifications only completely under Administration->General->Reset/Reboot to avoid any strange configurations if you've been playing around with this. I will talk through this assuming a default configuration with one recipient.

When you add one recipient, all event notifications are on for that recipient, by default, and will come every two minutes, until the condition clears. Since this is not really what you want to keep, I recommend going through and just disabling all events for every recipient so we can just turn on what events we want for each recipient.

  • To disable events for one or more recipients, go to Administration->General->Notification->By Group and select by group and make sure to select/tick the box next to Informational, Warning, and Critical.
  • Press Next, select Email Recipients, press next, and then select all of the recipients.
  • On the next screen (which is NOT the screen we should be checking on anything later because it always defaults back to the same thing), make sure to select the radio button for disable notifications.
  • Press apply and this action, once complete, will disable all notifications for all recipients as a starting point.

Now, let's do the critical notifications set up for recipient #2 and then you can follow this for the rest of the recipients that should receive informational and warning.

  • Go back to Administration->General->Notification->By group and select/tick the box next to critical only. Press next.
  • Select email recipients on the next screen and press next.
  • Select recipient #2 that should receive critical events. Press next.
  • On the next screen, this is where you should configure the 5 minute delay, 15 minute repeat interval, and tell it to repeat until the condition had cleared. (The radio button would also already say enable notifications. Also, as you can see, this screen defaulted to enable notifications, every two minutes, until condition clears. We had already gone through and disabled notifications so this screen is misleading in the fact that it is not the current configuration.)
  • Make sure to press apply to change and apply these new configurations.

Now, let's check this configuration. I'll show you the best spot, which is not ideal, but it is the best option.

  • Go to Administration->General->Notification->Byevent. I recommend clicking on the Power Events heading and then you'll be presented with all of the events.
  • On the right, there is an Event Log, Email, and Trap column. For Email and Trap, and if at least one of the recipients is configured to receive events, you'll see a bullet. You'll also notice that the events are sorted as Critical, Warning, Informational. From there, if you scroll a bit before clicking on any one event, you should see at this point, just a bullet in the email column for critical and nothing for warning and Information (yet).
  • Click on any one of the critical events towards the top for power events and you should see that your recipient #2 is enabled with the delay and frequency intervals.
  • You can also go back to Environmental Events and System events and review the current configuration too for Critical events in those categories.

Assuming this has been completed, then go through and select just informational and just warning for the respective recipients and you can go back in validate it under the By event screen.

If you're still stuck with this guidance, let me know.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
0
3175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

I have a feeling this may be working but since it is confusing where to actually look to validate it, you're being a little mislead which isn't you're fault. (This is something we're working to clarify and make easier to understand in future firmware revisions).

Here is what you should do or how I would do this and let me know if by what I say, you've found a difference in steps or have further questions.

I might recommend you reset Event Action notifications only completely under Administration->General->Reset/Reboot to avoid any strange configurations if you've been playing around with this. I will talk through this assuming a default configuration with one recipient.

When you add one recipient, all event notifications are on for that recipient, by default, and will come every two minutes, until the condition clears. Since this is not really what you want to keep, I recommend going through and just disabling all events for every recipient so we can just turn on what events we want for each recipient.

  • To disable events for one or more recipients, go to Administration->General->Notification->By Group and select by group and make sure to select/tick the box next to Informational, Warning, and Critical.
  • Press Next, select Email Recipients, press next, and then select all of the recipients.
  • On the next screen (which is NOT the screen we should be checking on anything later because it always defaults back to the same thing), make sure to select the radio button for disable notifications.
  • Press apply and this action, once complete, will disable all notifications for all recipients as a starting point.

Now, let's do the critical notifications set up for recipient #2 and then you can follow this for the rest of the recipients that should receive informational and warning.

  • Go back to Administration->General->Notification->By group and select/tick the box next to critical only. Press next.
  • Select email recipients on the next screen and press next.
  • Select recipient #2 that should receive critical events. Press next.
  • On the next screen, this is where you should configure the 5 minute delay, 15 minute repeat interval, and tell it to repeat until the condition had cleared. (The radio button would also already say enable notifications. Also, as you can see, this screen defaulted to enable notifications, every two minutes, until condition clears. We had already gone through and disabled notifications so this screen is misleading in the fact that it is not the current configuration.)
  • Make sure to press apply to change and apply these new configurations.

Now, let's check this configuration. I'll show you the best spot, which is not ideal, but it is the best option.

  • Go to Administration->General->Notification->Byevent. I recommend clicking on the Power Events heading and then you'll be presented with all of the events.
  • On the right, there is an Event Log, Email, and Trap column. For Email and Trap, and if at least one of the recipients is configured to receive events, you'll see a bullet. You'll also notice that the events are sorted as Critical, Warning, Informational. From there, if you scroll a bit before clicking on any one event, you should see at this point, just a bullet in the email column for critical and nothing for warning and Information (yet).
  • Click on any one of the critical events towards the top for power events and you should see that your recipient #2 is enabled with the delay and frequency intervals.
  • You can also go back to Environmental Events and System events and review the current configuration too for Critical events in those categories.

Assuming this has been completed, then go through and select just informational and just warning for the respective recipients and you can go back in validate it under the By event screen.

If you're still stuck with this guidance, let me know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
0
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

Your instructions worked. Thank you.

I have encountered one other issue. When I click to apply the changes, I sometime receive a browser error of "This page can't be displayed". At that point, I have to wait for the logon inactivity timeout before I can log back on to check if the change was successful or not. I am using Internet Explorer 10. Any ideas?

2399_display error.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
0
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

Hmm, no I haven't really seen that behavior. Although, I primarily use Chrome and rarely IE9 or Firefox.

When the page is like that and you refresh it, does it say somebody else is already logged in and that's why you have to wait for the timeout or is it completely inaccessible until auto-logout timer expires?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
0
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

Yes, it does say that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
0
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

The browser error seems to be less prevalent with Firefox. Additionally, while programming another AP9631 NMC with AOS 6.0.6, I have not experienced it at all.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

0 Likes
0
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:51 AM . Last Modified: ‎2024-03-05 12:09 AM

You definitely won't see it in 6.0.6 because one of the big features with it is multi-user so you can have multiple users and sessions simultaneously. Under control menu, I am forgetting off the top of my head, but i think there is an option there for session management so you could see the current sessions and also terminate them. So, you'd be able to see if multiple sessions were open. But you won't get told someone else is logged in unless you have so many sessions it can't support more (which is like 8-10).

Also, for you and any user on 6.0.6, I'd recommend apply 6.1.1 which has some critical bug fixes to take avdavantage of. And we have new release coming soon tentatively early August to fix bugs and provide 1-2 new minor features. It's available on our software/firmware download page which I know you can get to from apc.com/support. If you decide to upgrade the v5.1.7 some day to v6, there are also some FYIs regarding that major upgrade in our knowledge base also at apc.com. Let me know if you want further information or details.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore