Cannot add host to Host Protection UPS (PowerChute)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot add host to Host Protection UPS (PowerChute)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
hmi
hmi
Cadet

Posted: ‎2022-08-12 01:10 AM

0 Likes
3
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-12 01:10 AM

Cannot add host to Host Protection UPS (PowerChute)

Dear community,

 

I can see all hosts under PCNS -> Host Protection on the left side under my Data Center but I can not move it to the right side to match with the correct UPS.

 

I attached a screenshot - the hosts on the left side are greyed out and I can not drag and drop them.

 

We have 2 UPS and 3 Hosts

The main host (running PCNS and vCenter) is matched with the correct UPS, but I would like to match the the other hosts with the second UPS shown.

 

Am I missing something?

Any help would be greatly appreciated.

 

PCNS 4.4.3 and vCenter/ESXI 7

Attachments
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-08-12 12:51 PM . Last Modified: ‎2022-08-12 01:03 PM

0 Likes
2
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-12 12:51 PM . Last Modified: ‎2022-08-12 01:03 PM

@hmi 

 

Are you seeing a Red X when you drag the host to the UPS? If so that indicates you are attempting to add the host to the UPS, and you need to add the host to an outlet group. 

 

If the hosts are grayed out that indicates the host has been added to a UPS or outlet group. You will find the lists of assigned host in the pcnsconfig.ini file.

 

Examples

[advanced_ups_setup_0]
setup_name = SMT1500

hostlist = 192.168.0.141&1

 

[advanced_ups_setup_1]
setup_name = SMTL1000

hostlist = 192.168.0.176&1|192.168.0.144&1|192.168.0.128&1

 

 

Attachments
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

hmi
hmi
Cadet

Posted: ‎2022-08-12 09:46 PM . Last Modified: ‎2022-08-12 09:47 PM

In response to BillP
0 Likes
1
1074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-12 09:46 PM . Last Modified: ‎2022-08-12 09:47 PM

Thank you for the quick reply @BillP.

 

There is no red X, it's grayed out and there is just that forbidden icon (black crossed circle).

 

I checked the ini and I can see the following

 

hostlist = host1.domain.com|host2.domain.com

 

I noticed you have the '&1' in there. Is that mandatory?

I didn't edit the config manually before, so that is what the wizard put in there.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-08-16 09:23 AM

In response to hmi
0 Likes
0
1025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-16 09:23 AM

@hmi 

 

Try clearing the browser data, and then log in to the PowerChute UI. If the UI still does not display the hosts in the list, log out of the UI. Then log in to the PowerChute VM and stop the PowerChute service; the command is systemctl stop PowerChute. Next, edit the pcnsconfig.ini and remove the hosts from the list hostlist = host1.domain.com|host2.domain.com. Next, restart the PowerChute service (systemctl start PowerChute) and log in to the PowerChute UI. You should see the hosts available to add to the list.

 

To answer the question about the &number, that will be inserted if the associated UPS has switched outlet groups. In my example, I had each host associated with a UPS with outlet groups, and each was associated with group 1. 

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of