Can not get OpenSUSE Xen Dom0 to connect to APC SmartUPS 2200

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can not get OpenSUSE Xen Dom0 to connect to APC SmartUPS 2200
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
cboxall_apc
Crewman cboxall_apc
Crewman

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
4
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

Can not get OpenSUSE Xen Dom0 to connect to APC SmartUPS 2200

I'm going to start with saying that I know it is a long shot that anyone will be able to help me, but this seemed like a good place to ask.  So I spent my entire day beating my head into my desk trying to get this to work, with no success.  I am trying to get apcupsd to communicate via serial cable with my APC SmartUPS 2200.  I have gotten nowhere: apcupsd is installed but it can't connect to the UPS.  My preference is to connect using the on board serial port but will use the PCI Express serial port card if needed.

The last time I was able to get this to work was with the serial port card on a PowerEdge 6800 running OpenSuse Leap 42.1 as a Xen Dom0 (can't remember the exact Xen version).

To start, some specifics of the equipment involved -

Dell PowerEdge R510

APC SmartUPS 2200 with a broken USB port

Using a APC 940-0625A serial cable

Tried using the built in COM1 port

Also tried a PCI Express serial port card (don't have the exact model but can get it if it matters)

Xen 4.12 host

OpenSUSE 15.0 Dom0

Things I've tried -

UPSCABLE 940-0625A and UPSCABLE smart

UPSTYPE apcsmart and UPSTYPE dumb

DEVICE /dev/ttyS0 through DEVICE /dev/ttyS4

Disabled the Xen serial console by adding console=none to the GRUB_CMDLINE_XEN_DEFAULT line in /etc/default/grub and then running grub2-mkconfig -o /boot/grub2/grub.cfg

Verified the connections to the ports and the jack end on the APC

Checked to make sure COM1 was enabled in the BIOS and that the serial console option in the BIOS was disabled.  The BIOS has COM2 enabled for an internal serial port.

Disabled the agetty service from starting at boot to keep it from using COM1

lsof /dev/ttyS0 through lsof /dev/ttyS9.  All I get is for every port is -

lsof: WARNING: can't stat() fuse.gvfsd-fuse file system /run/user/1000/gvfs
      Output information may be incomplete.

I had also gotten a can't stat() message referring to /run/user/1000/doc for /dev/ttyS0, but that stopped after I stopped the agetty service.

The results of my setserial -g /dev/ttyS* command is -
/dev/ttyS0, UART: 16550A, Port: 0x03f8, IRQ: 4
/dev/ttyS1, UART: 16550A, Port: 0x02f8, IRQ: 3
/dev/ttyS10, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS11, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS12, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS13, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS14, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS15, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS16, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS17, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS18, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS19, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS2, UART: unknown, Port: 0x03e8, IRQ: 4
/dev/ttyS20, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS21, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS22, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS23, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS24, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS25, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS26, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS27, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS28, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS29, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS3, UART: unknown, Port: 0x02e8, IRQ: 3
/dev/ttyS30, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS31, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS4, UART: 16650V2, Port: 0xdcf8, IRQ: 40
/dev/ttyS5, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS6, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS7, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS8, UART: unknown, Port: 0x0000, IRQ: 0
/dev/ttyS9, UART: unknown, Port: 0x0000, IRQ: 0

Every apctest, and the log entries in /var/log/messages everytime I run apcupsd to try to start the daemon, all show the failure at the attempt to connect to the UPS.

This is for a home setup for local network, lab and hosting of Internet content.  The UPS is pretty old but I replaced the battery 2 years ago and it is in great shape (other than the broken USB port) so I'd really like to be able to use it.  

I really wanted to figure this out myself but just have had no luck at all.  Please help!  

Thanks ahead of time!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
1
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

Hi,

On 10/28/2018 9:29 PM, Colin said:

1) My SMT2200 is running firmware 7.1.  How can I tell if it can be updated to be able to use Modbus?  Also give that I only have a serial connection available on the unit, and it doesn't support modbus, how can I update the firmware?

The unit is not compatible with Modbus. 

On 10/28/2018 9:29 PM, Colin said:

2) The SMT2200 also came with a cable that connects to the serial port on the unit and has a USB port on the other end.  I've never used the cable before, so does it present another option for me to hook up the UPS to my server and / or update the firmware? 

Depending on the age of the SMT2200 it would ship with a 9 pin serial to RJ50 with the part number 940-0625 stamp on the 9 pin serial end. It would also ship with a standard USB A to USB B cable. If the cable you have has part number 940-0127 stamped on the USB end and the other end is RJ50 that cable is for a Back-UPS and is not compatible with the SMT. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
0
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

Hi,

APCUPSD does not support Serial communications to SMT2200, SMX2200, or SRT2200 Smart-UPS. The supported communications methods is USB or if the Smart-UPS is SMT or SRT2200 Modbus is also supported. Application Note 176 discusses Modbus implementation. 

Note: SMX2200 do not support Modbus communications and SMT2200 must be running firmware greater than UPS 09.0. 

Reply

Link copied. Please paste this link to share this article on your social media post.

cboxall_apc
Crewman cboxall_apc
Crewman

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
0
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

It looks increasingly like I'm going to have to get the add on card that includes a USB port (since the one built into the unit is broken).  However I do have some questions -

1) My SMT2200 is running firmware 7.1.  How can I tell if it can be updated to be able to use Modbus?  Also give that I only have a serial connection available on the unit, and it doesn't support modbus, how can I update the firmware?

2) The SMT2200 also came with a cable that connects to the serial port on the unit and has a USB port on the other end.  I've never used the cable before, so does it present another option for me to hook up the UPS to my server and / or update the firmware? 

I should mention that I do have a windows 10 PC to run firmware update software from if needed. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
1
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

Hi,

On 10/28/2018 9:29 PM, Colin said:

1) My SMT2200 is running firmware 7.1.  How can I tell if it can be updated to be able to use Modbus?  Also give that I only have a serial connection available on the unit, and it doesn't support modbus, how can I update the firmware?

The unit is not compatible with Modbus. 

On 10/28/2018 9:29 PM, Colin said:

2) The SMT2200 also came with a cable that connects to the serial port on the unit and has a USB port on the other end.  I've never used the cable before, so does it present another option for me to hook up the UPS to my server and / or update the firmware? 

Depending on the age of the SMT2200 it would ship with a 9 pin serial to RJ50 with the part number 940-0625 stamp on the 9 pin serial end. It would also ship with a standard USB A to USB B cable. If the cable you have has part number 940-0127 stamped on the USB end and the other end is RJ50 that cable is for a Back-UPS and is not compatible with the SMT. 

Reply

Link copied. Please paste this link to share this article on your social media post.

cboxall_apc
Crewman cboxall_apc
Crewman

Posted: ‎2022-07-01 03:26 PM

In response to BillP
0 Likes
0
1895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-01 03:26 PM

Finally got around to testing a shutdown!  Only years later.  LOL  Anyway, I ended up buying and installing a AP9620 for my APC.  Hooked up a regular USB cable from the card to my Xen server and the APC Monitor started working right away.  I had to move the server so I tried a UPS initiated shutdown (set the minimum power level to shutdown real high and unplugged the UPS).  Worked perfectly!  So a very belated thank you to everyone (here and on SpiceWorks) that helped me out!

  • Tags:
  • 2200
  • english
  • solved
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore