Can current Symmetra UPS handle c7000 HP blade enclosure?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can current Symmetra UPS handle c7000 HP blade enclosure?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:16 AM

0 Likes
4
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:16 AM

Can current Symmetra UPS handle c7000 HP blade enclosure?

Hello,

We have two L6-30 receptacles available that are evenly balanced on phases…except that the 2 circuits we have available to use are going to the APC that has a bad power module. It believe it already has a pretty high load on all phases, and if once we replace the power module, that the APC can still handle the load of the blades.

Will we be ok with the load? I did some research but I am stuck with what to really look at here? I have attached the picture from the power status of our Symmetra 40k...input current in amps?

The HP c7000 model we chose is the single phase chassis with 6 power supplies connect to two 208V 30AMP PDU’s that use a single L6-30P each (208V 30AMP circuit). Let me know if anyone can help...I am pretty lost with this.

Thanks.

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:15 AM

0 Likes
0
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:15 AM

To supplement that information, another one of our three-phase reps has chimed in with a little more insight:

From the image that is attached, this unit is approaching 100% (it's at 99% , specifically) power output delivered to the load - see Output kVA and Output VA at n+0. Only phase L2 shows some available wiggle room at 81% of total capacity. It it possible to connect 1kW worth of SINGLE-phase load to L2, or roughly 10A . It is not recommended that any additional load be placed on their UPS as it will, more than likely, go to static bypass due to an overload condition. The obvious side effect of going to bypass is that the load is no longer being protected by the UPS. It is highly recommended that the non-functioning power module be replaced/repaired prior to adding additional load.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:16 AM

0 Likes
0
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:16 AM

Here is a more detailed explanation of the enclosure if it helps: [http://h20000.www2.hp.com/bc/docs/support/SupportManual/c01543629/c01543629.pdf]

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:16 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:16 AM

I am having one of our three phase Symmetra experts look into your question. Bear with us for more information.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:15 AM

0 Likes
0
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:15 AM

EKrengel,

From the figures I see here, it looks like you currently have 2 working power modules installed.
I would suggest you add a 3rd power module to give your system N+1 redundancy with your current loads.

Reviewing the specifications of your HP c7000, it shows a maximum load of 8KVA
I would suggest you add a 4th power module to cover the additional load from the HP c7000.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:15 AM

0 Likes
0
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:38 AM . Last Modified: ‎2024-03-18 04:15 AM

To supplement that information, another one of our three-phase reps has chimed in with a little more insight:

From the image that is attached, this unit is approaching 100% (it's at 99% , specifically) power output delivered to the load - see Output kVA and Output VA at n+0. Only phase L2 shows some available wiggle room at 81% of total capacity. It it possible to connect 1kW worth of SINGLE-phase load to L2, or roughly 10A . It is not recommended that any additional load be placed on their UPS as it will, more than likely, go to static bypass due to an overload condition. The obvious side effect of going to bypass is that the load is no longer being protected by the UPS. It is highly recommended that the non-functioning power module be replaced/repaired prior to adding additional load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of