Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Can I connect an AP7921 to a SURT003 with an AP9871?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2804:57 AM. Last Modified: 2024-03-1803:56 AM
Can I connect an AP7921 to a SURT003 with an AP9871?
I'm checking whether I can connect an AP7921, which has an IEC-320 C20 socket, to the NEMA L6-20R socket on a SURT003 using the AP9871 cable.
My main concern is the outlet on the SURT003 is rated 20A and the cable and rack PDU is rated 16A. Will the PDU only draw what it needs from the socket? I'm just making sure before I do this as I don't want to fry anything.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2804:57 AM. Last Modified: 2024-03-1803:56 AM
The PDU and cable ratings are downrated in accordance with the NEC "80%" rule, which brings a 20a device current rating to 16a. The PDU plugged into the SURT003 will be fine, as the PDU will only pull its own max draw, which won't cause an issue with the SURT003's outlet.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2804:57 AM. Last Modified: 2024-03-1803:56 AM
The PDU and cable ratings are downrated in accordance with the NEC "80%" rule, which brings a 20a device current rating to 16a. The PDU plugged into the SURT003 will be fine, as the PDU will only pull its own max draw, which won't cause an issue with the SURT003's outlet.