Calculate inROW Power Draw for Genset or switchboard power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Calculate inROW Power Draw for Genset or switchboard power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
1
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:32 AM

Calculate inROW Power Draw for Genset or switchboard power

I'm troubled in how to calculate inRow power draw.

What I know:
APC inROW RP DX units consume over 20kW + 2kW condenser + 200w heating resistance (I don't know power factor), chilled water units 15kW each plus chiller plant.

What I wish to know:
1) Ratio between Datacenter Heat Output (in cooling kW) and and InRow Power Consumption (in kW) in DX or Chilled Water. I asume it is not linear.
2) In the event of power outage, from my experience every unit can be configured to start in sequence (whats the time limit?). How long does it take for the unit to reach normal operation once started? I would like to know how much time does it take to the unit after all its test to get in stationary mode. I also assume that when starting, the unit consumes full power, is that correct (compressors, blowers)?

So, for example, if I have a 4 inrow RP CW configuration, that will make (without chiller plant):

20kW x 4 Cooling power consumption = 80kW -> (PF 0,7) -> 115 kVA
Total Datacenter Heat Output is 45kW
Total IT Load (including UPS efficiency and battery chargers) 38kW -> (PF 0,8) -> 47.5kVA

It looks to me difficult to take the full 115 kVA as valid,


Are there any usage(%) or simultaneous(%) factors that I should take into account in order to properly dimension cooling switchboards and Genset? Are there tables or graphics of APC InRow units showing heat output vs power draw?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • calculate
  • consumption
  • genset
  • heat
  • inrow
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
0
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:32 AM

I'm troubled in how to calculate inRow power draw.

What I know:
APC inROW RP DX units consume over 20kW + 2kW condenser + 200w heating resistance (I don't know power factor), chilled water units 15kW each plus chiller plant.

What I wish to know:
1) Ratio between Datacenter Heat Output (in cooling kW) and and InRow Power Consumption (in kW) in DX or Chilled Water. I asume it is not linear.
2) In the event of power outage, from my experience every unit can be configured to start in sequence (whats the time limit?). How long does it take for the unit to reach normal operation once started? I would like to know how much time does it take to the unit after all its test to get in stationary mode. I also assume that when starting, the unit consumes full power, is that correct (compressors, blowers)?

So, for example, if I have a 4 inrow RP CW configuration, that will make (without chiller plant):

20kW x 4 Cooling power consumption = 80kW -> (PF 0,7) -> 115 kVA
Total Datacenter Heat Output is 45kW
Total IT Load (including UPS efficiency and battery chargers) 38kW -> (PF 0,8) -> 47.5kVA

It looks to me difficult to take the full 115 kVA as valid,


Are there any usage(%) or simultaneous(%) factors that I should take into account in order to properly dimension cooling switchboards and Genset? Are there tables or graphics of APC InRow units showing heat output vs power draw?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:32 AM

I'm troubled in how to calculate inRow power draw.

What I know:
APC inROW RP DX units consume over 20kW + 2kW condenser + 200w heating resistance (I don't know power factor), chilled water units 15kW each plus chiller plant.

What I wish to know:
1) Ratio between Datacenter Heat Output (in cooling kW) and and InRow Power Consumption (in kW) in DX or Chilled Water. I asume it is not linear.
2) In the event of power outage, from my experience every unit can be configured to start in sequence (whats the time limit?). How long does it take for the unit to reach normal operation once started? I would like to know how much time does it take to the unit after all its test to get in stationary mode. I also assume that when starting, the unit consumes full power, is that correct (compressors, blowers)?

So, for example, if I have a 4 inrow RP CW configuration, that will make (without chiller plant):

20kW x 4 Cooling power consumption = 80kW -> (PF 0,7) -> 115 kVA
Total Datacenter Heat Output is 45kW
Total IT Load (including UPS efficiency and battery chargers) 38kW -> (PF 0,8) -> 47.5kVA

It looks to me difficult to take the full 115 kVA as valid,


Are there any usage(%) or simultaneous(%) factors that I should take into account in order to properly dimension cooling switchboards and Genset? Are there tables or graphics of APC InRow units showing heat output vs power draw?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of