Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Battery questions
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2605:41 AM. Last Modified: 2024-03-1912:38 AM
Battery questions
Hi all
Our company has a new site going in at Angola and i have been asked a strange question which i have never had to think about before. Let me share some of the detail.
Power requirement - 5038VA
Runtime 15 hours!!!
Generator supporting site that will be running 8 hours a day Monday to Friday. At the weeked equipment onsite will be switched off.
I put the above figures into the APC UPS calculator and i receive the following recommendation.
APC Smart-UPS VT rack mounted 30kVA 400V w/4 batt mod. exp. to 5, w/PDU & startup
SUVTR30KH4B5S
3 x APC Smart-UPS VT Extended Run Enclosure w/6 Batt. Modules and 5x8 Startup Service
SUVTXR6B6S
My main questions are....
How will the batteries be affected by constant discharging and regharging each day?
Will there be enough time in the day (8 Hours) to rechange all of the batteries and bring it back up to full capacity before the generator is switched off?