- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Battery Constant for SU3000RMXL3U
I just recently purchased two units. After replacing the batteries an unusually low time shows remaining.
I am hopeful someone can share the Battery Constant value for these units.
Thanks.
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:51 PM
Hi, thanks for your response. I consulted the local services and they did not answer me. Greetings and many thanks
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Sigh..... I seem to be sharing the same frustration others have experienced. I contacted support for the value, and the claim is they no longer have this information.
Angela, can you help ???
Thanks
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
I'll give it to you at your own risk. We are working on stocking more calibration keys in the next few weeks and that will be the future solution that we offer. (It is a dongle that connects to your UPS serial port and changes the constant automatically). We don't really give constants out anymore because people can brick their UPS if the process is done incorrectly and we cannot be liable for that. You are also only supposed to do this procedure when the batteries are new (for anyone else that comes across this). '52' is the value you need.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Thank you very much. That is excellent news, and I appreciate the code. On another well used list which is out there on the 'net the value is different. Good to have the verified code.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Wait. So what exactly is the solution here ? I have 5 x SU3000RMXL3U ,and I replaced the battery modules last week on one and now I have a inappropriately low runtime. I want to make sure I have a solution going forward before I change out the modules on the other 4.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
This should be reviewed first Ryan -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156538 as it will likely cover the situation you're talking about and what Rob was talking about. And then if that doesn't work, you may find information about a "battery constant" online that may need to be reset. We stopped giving out the procedure publicly because if done improperly, you can brick your UPS.
We will be producing calibration keys for users as a convenience in the near future so that you don't have to embark on the manual reset of the battery constant.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Thanks again Angela. Both units successfully changed and now reflecting the expected durations.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:52 PM
Thanks for the info. Will a apc 940-0625A cable work for the procedure? And I hope you inform us when the dongle is ready. Thanks again.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:52 PM
No, you need 940-0024 or 940-1524. 940-0625 is only used with newer types of UPS models where this procedure does not apply.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:52 PM
It seems I made a mistake in my model # , I have the SURTD3000RMXL T3U and it recently got the battery modules replaced and is reading the wrong runtime. Does "the procedure" still apply ?
Sorry to hijack your thread Bob.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
No, the procedure nor the specific issue of having to potentially manually reset the runtime applies to that model of UPS. You'll want to review that knowledge base link I sent for options on this model and confirm what amount of runtime is reported versus what should be reported. Your first step as described there will likely just be a standard runtime calibration.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
Thanks clearing up my confusion. I'll review the material once again and create a new thread if I need further assistance. Thanks again
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
Dear Angela, I changed the whole battery pack of my APC Smart-UPS 2200 RM XL (SU2200RMXLI3U), serial number is JS0929007192.
Unfortunately, I'm unable to charge those batteries. When Powerchute shows 100% and I start a self-test it stops immediately
lighing up the 'overload' led. I tried to change battery constant and leaving time to charge with no load attached by using value '8C', 'AF', and 'A0'
but without results.
Could you please help me?
my email is shivahpc at gmail dot com
Best
GS
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
Hello Angela.
Hello guys.
Does anyone knows the battery constant parameter for a surt6000xli
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
hello Hans, that kind of calibrations can be done only by official services,
regards,
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
Dear Angela, I have the same problem with an SRC3000XLI S / N: B21151001408, could you give me the value of the constant? Thank you so much
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:52 PM
Hi Juan -
You should contact your local tech support team for assistance with this.
thanks
Liam
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:47 PM . Last Modified: 2024-03-18 11:51 PM
Hi, thanks for your response. I consulted the local services and they did not answer me. Greetings and many thanks
Link copied. Please paste this link to share this article on your social media post.

