BX1500M is battery hot swappable?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • BX1500M is battery hot swappable?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Disneysnob
Disneysnob
Cadet

Posted: ‎2025-09-09 02:33 PM

0 Likes
1
346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-09 02:33 PM

BX1500M is battery hot swappable?

I have the BX1500M unit and it is needing a battery replacement.
Can the battery be hot swapped, or does the unit need to be completely powered down first?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2025-09-10 02:06 AM

1 Like
0
344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-10 02:06 AM

Short Answer: No, this hardware is not designed to be hot swappable.

 

Long Answer: Any unit that is hot swappable is designed with firmware, electronically, and physically to allow the end user to easily replace the RBC.

 

It does not require the unit to be turned over or remove a battery terminal such as a Molex connector. All hot swappable units have a front facing bezel that is accessible and typically use a Anderson quick disconnect connector.

 

Having said all the above depending upon firmware and hardware topology you can take a chance and see if the unit drops the output load upon the RBC being disconnected while AC Mains is connected.

 

If this is the larger 24 VDC capacity unit with two cells tied together with a plastic plate and sticker. It’s easier and safer to remove and eject as the battery terminals are shrouded and pose no danger to end user. As you’re simply pushing the entire RBC into the housing and never touching the battery terminals.

 

If this is the smaller version where you have to disconnect the positive battery terminal you’ll want to take great care while doing so.


As the system is actively outputting DC voltage at the terminal.

 

NOTE: If this system is connected to a computer that is running APC Power Chute / NUT / shutdown application.

 

Ensure you disconnect the USB cable to avoid the graceful shutdown sequence. 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2025-09-10 02:06 AM

1 Like
0
345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-10 02:06 AM

Short Answer: No, this hardware is not designed to be hot swappable.

 

Long Answer: Any unit that is hot swappable is designed with firmware, electronically, and physically to allow the end user to easily replace the RBC.

 

It does not require the unit to be turned over or remove a battery terminal such as a Molex connector. All hot swappable units have a front facing bezel that is accessible and typically use a Anderson quick disconnect connector.

 

Having said all the above depending upon firmware and hardware topology you can take a chance and see if the unit drops the output load upon the RBC being disconnected while AC Mains is connected.

 

If this is the larger 24 VDC capacity unit with two cells tied together with a plastic plate and sticker. It’s easier and safer to remove and eject as the battery terminals are shrouded and pose no danger to end user. As you’re simply pushing the entire RBC into the housing and never touching the battery terminals.

 

If this is the smaller version where you have to disconnect the positive battery terminal you’ll want to take great care while doing so.


As the system is actively outputting DC voltage at the terminal.

 

NOTE: If this system is connected to a computer that is running APC Power Chute / NUT / shutdown application.

 

Ensure you disconnect the USB cable to avoid the graceful shutdown sequence. 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore