BE650G2-UK Shuts down on power outage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • BE650G2-UK Shuts down on power outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Birchcroft
Crewman Birchcroft
Crewman

Posted: ‎2025-02-03 01:26 AM . Last Modified: ‎2025-02-03 01:29 AM

0 Likes
5
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-03 01:26 AM . Last Modified: ‎2025-02-03 01:29 AM

BE650G2-UK Shuts down on power outage

my BE650G2 shutdown immediately after a power cut.  On restoring power I checked its status using PowerChute-Serial Shutdown.  This showed:

System Status

    Device Status:  On Line, Battery Discharged

    UPS Load 15%

    Runtime Remaining 0 Minutes

 

Battery Status

    Battery Charge 100.0%

    Battery Voltage 13.6VDC

 

The data log also indicates that the battery charged overnight.

 

Also when I tried to run the self diagostics it returned with status: Refused

I've attached screen shots of the status and data log pages.

 

Please can anyone suggest what the problem may be?

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Spock Teken
Spock

Posted: ‎2025-02-03 05:58 AM . Last Modified: ‎2025-02-03 06:00 AM

0 Likes
3
671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-03 05:58 AM . Last Modified: ‎2025-02-03 06:00 AM

Based on the limited information the battery is flat and needs to be replaced. Provide the serial number and when the unit was purchased and commissioned into service.

 

The battery cartridge has a average service life of 2-5 years. Based on usage, temperature, and environmental conditions.

 

If the system falls within this range it’s time to replace the battery cartridge with a high quality (HR) rated cell / cartridge or what APC terms a RBC.

 

A RBC is simply a Replacement Battery Cartridge. Your system takes a RBC110 which is just a standard 12 VDC / 7 AH cell.

 

You may install any 7, 7.5, 8, 9, 10 amp hour cell in the same form factor. Lastly, one of the OEM battery makers is CSB.

 

As such look for a reseller in your region selling the same.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Birchcroft
Crewman Birchcroft
Crewman

Posted: ‎2025-02-04 12:03 AM

In response to Teken
0 Likes
2
642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-04 12:03 AM

Hi Teken

 

Thanks for the response which confirms what I suspected.

However, if it is that the battery needs replacing then I have to say I am a bit on the disappointed side for the following reasons:

  1. The UPS is in a benign environment with a temperature range of 15-22 DegC so it shouldn't really impact battery life too much.
  2. This is the first time it had to cut in since installation back in 04/2022 and it failed without warning.
  3. The inidcator lights on the front pannel do not indicate that the battery needs replacing.
  4. The manual gives the battery life as 3-5 years.  It was installed 04/2022 so it hasn't reached the age range specified by Schneider.

So all in all while I suspect you are right I find it dissapointing that the unit should fail without warning, which is what makes me think there is a chance something else is amiss.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-02-04 01:42 AM

In response to Birchcroft
0 Likes
1
634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-04 01:42 AM

Based on the information you provided regarding the installation date. You just missed the two year warranty coverage. ☹️

 

I would encourage you to purchase a new battery to see the results. In the interim if your specific unit has a data port connect it to a computer running the APC Power Chute software via the supplied USB cable.

 

Once the two are connected and running it may be able to provide more insight to the active fault / error code(s). Depending upon version of PCPE / PCSS software it may provide the following event, data, ups logs.

 

If so, please do share the same here for review if possible. 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Birchcroft
Crewman Birchcroft
Crewman

Posted: ‎2025-02-05 12:26 AM

In response to Teken
0 Likes
0
572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-05 12:26 AM

After the fault occured I installed PowerChute Serial Shutdown.  Attached are some screen shots of the log from yesterday.  From the data log you will see that the UPS load is low, this is because I now, until I get a new battery, turn off the systems when not in use.  The normal load is around 35 to 40%.

 

Screenshot 2025-02-04 at 11-36-54 Data Log.png

Screenshot 2025-02-04 at 11-35-04 Event Log.png

Screenshot 2025-02-04 at 11-33-28 UPS Status.png

   

Reply

Link copied. Please paste this link to share this article on your social media post.

Birchcroft
Crewman Birchcroft
Crewman

Posted: ‎2025-02-05 03:28 PM

0 Likes
0
572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-05 03:28 PM

Teken I've tried a couple of times to respond to your post but the forum seems not to be working properly with Firefox, or at least the way I have it configured.  So I'm trying again with Chrome which seems to work better with the forum.

 

After the problem occurred I installed PowerChute-Serial Shutdown which is what is providing the contradictory information, ie that the battery is both discharged and 100% charged.  All status lights are solid green.  I've attached screen shots of the Event Log, Data Log, and UPS Status.  You will notice that the Data Log shows the battery charge  dropped to 39% at one point.  I am confident that this was due to a brown out/momentary voltage drop.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of