Are there GFCI with UPS?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Are there GFCI with UPS?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:03 AM

0 Likes
5
4060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:03 AM

Are there GFCI with UPS?

A related concern we have is with the combination of UPSs and GFCIs. Blindly plugging a UPS on to a GFCI protected socket defeats the protection the GFCI provides. We have the small/medium  APC UPS across our campus, what is your opinion and recommendation on this moving forward?

 

    As we see it, UPS protects the equipment and GFCI protects humans. So we need a consistent approach to establish guidelines of utilization of both. Are there GFCI-protected UPSs?

 

    Let us know what you think. Please do the needful ASAP.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
0
4055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

Hello - 

On battery mode the UPS will have a floating Neutral, which would likely trip any GFCI you were to plug into the UPS. These units are only designed for dry, climate controlled applications and should never be used near water, outdoors, or any place that you would traditionally use GFCI protection. I am not aware of any UPS manufacturer that has GFCI protection on the output.

Thanks,

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:03 AM

0 Likes
0
4055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:03 AM

Hello - 

It is possible to use a UPS with a GFCI outlet, however due to the types of load attached to the UPS as well as the way UPS and surge products function, they do exhibit leakage currents. These currents are a natural result of the common mode filters present in computers and UPSs. These leakage currents may be large enough to "fool" the GFCI and cause it to trip. If this is what you are experiencing, you may need to replace the GFCI outlet or try a different brand/model. It might be worth following up with the vendor of the GFCI product to see if they have any models that they recommend for use in this type of environment.

This issue is documented in our knowledge base document #FA158850

You can access it here: http://www.apc.com/us/en/faqs/index?page=content&id=FA158850

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:03 AM

0 Likes
0
4055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:03 AM

Dear Liam, Thanks for your response.

While working Battery mode operation, How the GFCI can protect the UPS on downstream side to the connected loads. What is the safety for the humans?

What precaution have to take to protect the human from UPS exhibiting leakage current,while working on battery operation?

 Let me know,the necessity steps to take?

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
0
4055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

Liam is right. 

We are electricians and we just change the GFCI outlet to GFCI type breakers if GFI is really needed.  Most GFCI outlets were installed by the lowest bid contractor, using the cheapest labor, and lowest quality parts, and that was riding around in a van for a year.  GFCI breakers are 100x more reliable. 

Also, maybe reconsider placement of the UPS.  Keeping the UPS is a fixed place, protecting only fixed loads, and in a secure setting reduces many of the issues that GFCI option protects against.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
0
4055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

Dear Liam & Bob,

Thanks for your response,

Yes. You guys are right. I am accepting it, but i need a small clarification.

While on battery mode operation, If the leakage current is exceed the limit, How we can protect the human? In ups itself have any self protection to shutdown on loads?

Kindly reply me back.. Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
0
4056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-18 12:02 AM

Hello - 

On battery mode the UPS will have a floating Neutral, which would likely trip any GFCI you were to plug into the UPS. These units are only designed for dry, climate controlled applications and should never be used near water, outdoors, or any place that you would traditionally use GFCI protection. I am not aware of any UPS manufacturer that has GFCI protection on the output.

Thanks,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of