Anybody using or used APC PDU before? Amp meter displays zero

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Anybody using or used APC PDU before? Amp meter displays zero
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

0 Likes
7
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

Anybody using or used APC PDU before? Amp meter displays zero

Hi, I am newbie at this, I purchased a ap7900, I plugged in electronics and computer to it, but the amp meter always display zero, I pressed and hold the black button for 5 seconds, it cycles through some meaningless numbers and then go back to zero again.

do i need to run some script to it or did i receive a lemon?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:28 PM

0 Likes
0
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:28 PM

Hey, thanks and you are right, desktop laptops routers do not draw large current I am so dumb.
I was testing it and was only plugging in electronics while they are in idle state, never really test them under heavy working condition.
so I decide to plug in a laserjet and print a page and the amp meter shows 3 amps immediately.

Thanks again i got it now.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

0 Likes
0
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

"a desktop computer, routers, and laptop" is not a big load in terms of Amps.
Do you have more large load to connect?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

0 Likes
0
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

Hello, sf1
Could you check the following:
1) Status LED
2) If the PDU is properly configured ( for eg you can get access to online menu via web-browser)
http://www.apcmedia.com/salestools/ASTE-6Z6KAM_R0_EN.pdf
3) Try to add more load ( for eg current should be more then 3 Amps)
I would assume that the load is too small to read it from the display

What will be the results?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

0 Likes
0
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

Hi, the status LED is green which is ok,
i configured the ip setting so i can access the PDU settings with my laptop
I also tried plugging in a desktop computer, routers, and laptop to the outlets the amp meter shows zero

Message was edited by: sf1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

0 Likes
0
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

when you log into the PDU, does it tell you how many amps the PDU is providing in there? it should be on the main (home) screen when you log in with a little colored bar that is green, yellow, or red. it will also give you details under the device manager section. (this is assuming that it is the newer firmware which I think is a safe assumption i think).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

0 Likes
0
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:29 PM

Hi, it is the same thing when i log on,
front page and device manager both display
load status 0.0 amps [normal load]

where do i check version & flash new firmware?

thanks.

Message was edited by: sf1

Message was edited by: sf1

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:28 PM

0 Likes
0
2552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:28 PM

The current version would be under Administration - General - About. It's probably 3.x, with the light blue background screen.

However, the new revision is here:

http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=SFRPDU358

The firmware probably won't have a change on the display registering a load however.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:28 PM

0 Likes
0
2553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:14 AM . Last Modified: ‎2024-02-14 10:28 PM

Hey, thanks and you are right, desktop laptops routers do not draw large current I am so dumb.
I was testing it and was only plugging in electronics while they are in idle state, never really test them under heavy working condition.
so I decide to plug in a laserjet and print a page and the amp meter shows 3 amps immediately.

Thanks again i got it now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore