An internal UPS communication fault exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • An internal UPS communication fault exists
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ADAC-NBY
Crewman ADAC-NBY
Crewman

Posted: ‎2025-09-16 07:38 AM

0 Likes
3
580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-16 07:38 AM

An internal UPS communication fault exists

Hi, i get this error/alarm: An internal UPS communication fault exists.

 

I found the followingarticle on this topic: https://www.apc.com/us/en/faqs/FA241461/ 

But where can I get this specific update procedure?

Model: Smart-UPS 1000
SKU: SMT1000RMI2U
Serial Number AS1106120XXX
Network-Card Model Number: AP9630
Name: sumx Version v7.2.2
 

We have several of these UPS units in use with the same NMC2 card. But one UPS unit is producing this error.

Can anyone here help me, please?

Best regards,

Steffen

 
  • Tags:
  • Englisch
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2025-09-17 03:23 AM

0 Likes
0
578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-17 03:23 AM

That APC FAQ applies only to a SMX Series with UPS ID11.

 

https://www.apc.com/us/en/faqs/FA279197/


Based on the information you have provided the unit on site is a SMT Series produced in June 2011 . You’ll need to provide the serial number, UPS ID, from the NMC About tab for both NMC / UPS.

 

Along with the following logs in their entirety minus any PI data which you can remove / delete: Event, Data, UPS, Diagnostic.

 

In the interim you can roll the NMC 2 back to 5.X.X ~ 6.X.X firmware to see if the communication fault clears.

 

If the error goes away this unit will need to remain on this specific NMC firmware. The hardware is 14 years old and should have been refreshed four years ago.

 

https://www.se.com/au/en/faqs/FAQ000265093/

 

Assuming this firmware applied to your specific model UPS. You have a better than 75% chance of bricking this hardware during the firmware update process! ☝️

 

Given it’s way out of warranty you would have a very heavy and expensive paper weight.

 

NOTE: Validate the problem remains by swapping the NMC / removing it. You may also complete a Brain Dead reset to see if it clears the issue by following this APC Resource Link and report back the results:

 

https://www.apc.com/ca/en/faqs/FA156611/

 

Questions Ask . . . 👍

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2025-09-17 03:23 AM

0 Likes
0
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-17 03:23 AM

That APC FAQ applies only to a SMX Series with UPS ID11.

 

https://www.apc.com/us/en/faqs/FA279197/


Based on the information you have provided the unit on site is a SMT Series produced in June 2011 . You’ll need to provide the serial number, UPS ID, from the NMC About tab for both NMC / UPS.

 

Along with the following logs in their entirety minus any PI data which you can remove / delete: Event, Data, UPS, Diagnostic.

 

In the interim you can roll the NMC 2 back to 5.X.X ~ 6.X.X firmware to see if the communication fault clears.

 

If the error goes away this unit will need to remain on this specific NMC firmware. The hardware is 14 years old and should have been refreshed four years ago.

 

https://www.se.com/au/en/faqs/FAQ000265093/

 

Assuming this firmware applied to your specific model UPS. You have a better than 75% chance of bricking this hardware during the firmware update process! ☝️

 

Given it’s way out of warranty you would have a very heavy and expensive paper weight.

 

NOTE: Validate the problem remains by swapping the NMC / removing it. You may also complete a Brain Dead reset to see if it clears the issue by following this APC Resource Link and report back the results:

 

https://www.apc.com/ca/en/faqs/FA156611/

 

Questions Ask . . . 👍

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

ADAC-NBY
Crewman ADAC-NBY
Crewman

Posted: ‎2025-09-17 11:26 PM

0 Likes
1
558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-17 11:26 PM

Hi Teken, after 2 days the UPS has Restored the local network management interface-to-UPS communication. But i dont know why. 

 

Thanks for you help.

 

Best regards 

Steffen 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-18 09:44 AM

In response to ADAC-NBY
0 Likes
0
547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-18 09:44 AM

You’ll want to check the logs and monitor the NMC at random intervals for the following:

 

Cold start, email sent errors, can’t login to the internal website.

 

Cold starts (Self Boot) can happen when there are connectivity issues. The NMC has a watch dog timer as such if it can’t communicate properly it will self boot.

 

If you can’t login or takes a long time for the page to load. Along with seeing error messages of emails not being sent.

 

This and self boots are related to a endless bug APC hasn’t fixed which are called out in the NMC Firmware Release Notes.

 

Essentially the system is over loaded with processes and results in a hang / lock. This problem wasn’t present or noticeable in 7.1.8 and prior firmware but very much so in 7.2.0 - 7.2.2! 🤦‍♂️👎

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore