I m getting an alarm on an In row cooling unit ''Water detection fault''.
Can any one, let me please understand the nature of alarm? what this alarm is for?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:07 AM . Last Modified: 2024-03-18 11:39 PM
Thanks a lot..
It got it that there was no any leakage in the bottom/around the rope...
It was cloudy/rainy weather here, and many units giving high humidity alarms and this was also due to the high humidity..
So again thanks for clarification..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:07 AM . Last Modified: 2024-03-18 11:39 PM
Hello Abdul. This Water Detection Fault alarm means that the leak rope sensor connected to the Inrow unit detected water. Check around the bottom of the unit and where the leak rope is located to see if there is any water visible around the rope. If there is, see if you can locate where the water is coming from. If there is no water, check the connection for the leak rope to make sure it is secure and clear the alarm. Watch the unit to see if the alarm returns. If there is water or the alarm returns, please call into your local tech support to get further assistance in finding the leak.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:07 AM . Last Modified: 2024-03-18 11:39 PM
Thanks a lot..
It got it that there was no any leakage in the bottom/around the rope...
It was cloudy/rainy weather here, and many units giving high humidity alarms and this was also due to the high humidity..
So again thanks for clarification..