Amp display on switched rack PDU - error codes - what do they mean?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Amp display on switched rack PDU - error codes - what do they mean?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:18 AM

0 Likes
6
4807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:18 AM

Amp display on switched rack PDU - error codes - what do they mean?

We have recently installed a couple of the vertical 3 phase, 24 port PDUs.

On many of them, the Amp display, for phase 2, does not show a number, but "E". Not "Er", just "E"

Looked around and cannot find a page on the apc web site where this is documented.

Also, on two of the PDUs, one or more of the phases displays an "L"

Any hint on what this means?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • errors
  • pdu
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:18 AM

0 Likes
0
4808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:18 AM

The only thing the display should show is "88" when its initializing or "Er" when there is a fault or something.

are you able to login and check the amperage readings via the web interface? it is possible that the display is inverted and you are actually seeing "3" and "7" or something indicating how many amps are being drawn from that phase.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:18 AM

0 Likes
0
4809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:18 AM

The only thing the display should show is "88" when its initializing or "Er" when there is a fault or something.

are you able to login and check the amperage readings via the web interface? it is possible that the display is inverted and you are actually seeing "3" and "7" or something indicating how many amps are being drawn from that phase.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

0 Likes
0
4811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

On 4/29/2009 4:16 PM, Angela said: The only thing the display should show is "88" when its initializing.
Good Morning Angela,
I have a PDU that has been working fine for years, but it is now showing "88" on the display, and you cannot switch between phases to see the amperage. everything is still powered up, but that PDU has been showing "88" for several Hours now. I am concerned that it is about to Kack? what do you mean initializing?
Also do you know of somewhere on the site that I can find a Lexicon of Error Codes?
Thanks Andres

 

  • Tags:
  • 88
  • code
  • display
  • pdu
  • rack
  • switched
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

0 Likes
0
4811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

Hi,

What is the model number of the PDU?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

0 Likes
0
4810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

Hello Bill,

 thanks for the reply, I will need to do some digging as the Bar is installed and the model number is on the back. I'm sure I could get it via a utility to log into the PDU with a console cable? but I don't think we have that. None the Less I can check old records and we have that info from Our inventory. Let me get back to you. Thanks for your interest and any assistance, you choose to offer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

0 Likes
0
4811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

Ok, Bill,

So, unfortunately, the PDU is in operation and attached to the rack so I cannot see the back of it where the Model number is located. I was able to find the inventory sheet and have the serial number for the PDU but no model number. Do you know if there is a Search Tool on the APC website that I could plug in the serial number and get that information?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

0 Likes
0
4811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:37 AM . Last Modified: ‎2024-03-18 04:17 AM

Hi Andres,

For any model PDU that uses that style display, showing "88" happens either when the display is initializing (after being first turned on), or if it is unable to load past the initial boot. If it continues to display "88" after a power cycle, then the only thing to try would be a firmware upgrade to rule out any communication issues. If it's still not working after that, then the device would need to be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore