Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

After replacing an NMC2 with an NMC3, what additional steps are required in PCNS?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • After replacing an NMC2 with an NMC3, what additional steps are required in PCNS?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
LarryK
Lieutenant LarryK
Lieutenant

Posted: ‎2022-07-18 12:48 PM

0 Likes
1
305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-07-18 12:48 PM

After replacing an NMC2 with an NMC3, what additional steps are required in PCNS?

I will be replacing NMC2 cards with NMC3 cards next month.

 

At some sites, PCNS is installed.


Looking for specific steps to perform in the software following the change in hardware.

 

Thanks!

  • Tags:
  • english
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-08-18 07:22 AM . Last Modified: ‎2022-08-18 07:38 AM

0 Likes
0
209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-08-18 07:22 AM . Last Modified: ‎2022-08-18 07:38 AM

@LarryK 

 

 

First, on the NMC, you will need to add the PowerChute user name and authentication phrase and enable HTTP or HTTPS to allow communication with the NMC. 

 

PowerChute Shutdown Parameters firmware 6.8.png

 

Next, you will need to register the PCNS clients with the new NMC. You can do that by running the PowerChute Setup from the UI or editing the pcnsconfig.ini file.

PowerChute Setup Tab Selected.png

 

pcnsconfig.ini example:

[NetworkManagementCard]
mode = single
IP_1 = 192.168.0.128
port = 443
protocol = https
enrolWithNMC = true
acceptCerts = true
IP_1_Outlet = 1

 

After editing the pcnsconfig.ini file, you will need to stop and restart the PowerChute service to allow the PowerChute client to register with the new NMC. 

See Answer In Context

  • Tags:
  • english
Reply
Share
Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-08-18 07:22 AM . Last Modified: ‎2022-08-18 07:38 AM

0 Likes
0
210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-08-18 07:22 AM . Last Modified: ‎2022-08-18 07:38 AM

@LarryK 

 

 

First, on the NMC, you will need to add the PowerChute user name and authentication phrase and enable HTTP or HTTPS to allow communication with the NMC. 

 

PowerChute Shutdown Parameters firmware 6.8.png

 

Next, you will need to register the PCNS clients with the new NMC. You can do that by running the PowerChute Setup from the UI or editing the pcnsconfig.ini file.

PowerChute Setup Tab Selected.png

 

pcnsconfig.ini example:

[NetworkManagementCard]
mode = single
IP_1 = 192.168.0.128
port = 443
protocol = https
enrolWithNMC = true
acceptCerts = true
IP_1_Outlet = 1

 

After editing the pcnsconfig.ini file, you will need to stop and restart the PowerChute service to allow the PowerChute client to register with the new NMC. 

  • Tags:
  • english
Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc