New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
After replacing an NMC2 with an NMC3, what additional steps are required in PCNS?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
First, on the NMC, you will need to add the PowerChute user name and authentication phrase and enable HTTP or HTTPS to allow communication with the NMC.
Next, you will need to register the PCNS clients with the new NMC. You can do that by running the PowerChute Setup from the UI or editing the pcnsconfig.ini file.
After editing the pcnsconfig.ini file, you will need to stop and restart the PowerChute service to allow the PowerChute client to register with the new NMC.
First, on the NMC, you will need to add the PowerChute user name and authentication phrase and enable HTTP or HTTPS to allow communication with the NMC.
Next, you will need to register the PCNS clients with the new NMC. You can do that by running the PowerChute Setup from the UI or editing the pcnsconfig.ini file.
After editing the pcnsconfig.ini file, you will need to stop and restart the PowerChute service to allow the PowerChute client to register with the new NMC.