Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Accidentially cleared EEPROM on Smart-UPS 5000RM (SUA5000RM I5U)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Accidentially cleared EEPROM on Smart-UPS 5000RM (SUA5000RM I5U)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
160
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
9
4780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 AM . Last Modified: ‎2024-03-17 11:12 PM

Accidentially cleared EEPROM on Smart-UPS 5000RM (SUA5000RM I5U)

Hello there,

I have an APC Smart-UPS 5000 RM I5U with a NMC 9617. I recently replaced the batteries a few months before and did the runtime calibration a couple of times. My original problem was that the UPS had very little runtime at a load of 9 % (only like 20 minutes). I did some googling and stumbled across the Battery constant issue. I´ve decided to give it a shot...well, afterwards you always learn something for the future.

I did follow the guide over at http://joeteck.com/apc.htm. I fired up a Windows XP with Hyperterminal, connected to the UPS with no issues, got into the PROG mode and accidentially pressed strg+y, which cleared the EEPROM. Now the UPS thinks that it is a Smart-UPS 450, wrong voltages and wrong line frequency etc. 

I want to make clear at this point that I understand that this is a absolute no-go action by going into the PROG mode and messing around with stuff, I was aware of the dangers of my action. The only thing I want to ask here is if there´s a chance to get this thing working again by setting again the correct values for the model etc. I already managed to set the correct model and could confirm that the voltages (I live in Germany) were correct. The current issue is that the line frequency is wrong and it´s not recognizing the input power => when I turn on the input power, it still remains on battery, complains about a line failure and shows the wrong line frequency (60 instead of 50). A friend of mine who is an electrician disassembled the UPS and checked if there were damages to the electrical parts. As far as he could test it, there were no damages.

I am also thinking of getting a dump of the EEPROM somewhere and cloning it to my EEPROM, but it seems that no one has put a dump of it online. If anyone here has the same model like me and would not mind dumping its contents, please get in touch with me.

Every little advice would help.

Kind regards

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

On 1/31/2019 4:15 AM, Brad said:

Are you *sure* that's an SUA? The firmware code looks more like a 3rd generation SU.

With a manufacture date of 2001 it's be in a gray area.

The UPS I got the values from are exact the same model.

The manufacturing date is not real, just something I´ve put in temporarily until I´ll figure out the real one. Same goes for the battery replacement date.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 AM . Last Modified: ‎2024-03-17 11:12 PM

Is there anyone who had a similiar issue? Come on...

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Brad_C
Contributor

Posted: ‎2021-06-28 09:36 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 AM . Last Modified: ‎2024-03-17 11:12 PM

Whoops. Yes I had an SU1400RM that lost its mind and I had to rebuild the eeprom. The SUA has extra constants that I haven't had the need to play with (VA vs Watts for instance).

Where you will likely run into serious issues are the constants 4, 5 & 6. These are undocumented and there exists a little list of the known ones in the apcupsd documentation. There are none listed for an SUA5000. They are fundamental to the way the UPS responds to its batteries and getting them wrong leads to all sorts of major behavioural issues on battery.

If you had those then you could calibrate the voltages, loads, VA measurement and other variables to get it back to mostly working. Without those you're pretty much in the dark. If you knew someone with an identical unit they could read them out for you.

The 50/60Hz thing is indicative of it thinking it's a "domestic" machine rather than "International". In the SU series that was defined by the model code. I can't help you with how it works on the SUA.

Your biggest immediate issue will be without a correctly set battery voltage scaling constant the UPS is quite likely to be under-reading the battery voltage and winding the charge output up to compensate. That'll cook your batteries in short order.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

Thanks for your info. That means I have currently two options: Getting a dead throwaway ups from ebay or get in touch with someone who has the correct values for the smart constants.

Option 1 is currently not the one for me as on ebay the 5000 RM is still quite expensive, even the dead ones, and option 2 isn´t available to me either because I don´t know someone who has the same UPS as mine, which brings me to my question:

Can someone here in the forum who has the same UPS model as mine dump me the values?

I´m currently using this tool (http://apc-fix.com) to fight my way back to the correct settings and I´ve already requested the full version.

You can use it to read out nearly everything important (and in this case the Smart Constants too), it looks like this:

mgDuOtSbmasOe3oja6upeQ%3D%3D.jpegmgDuOtSbmasOe3oja6upeQ%3D%3D.jpeg

If anyone can provide me the correct values would be great.

Kind regards to you Brad for the response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

Hi Brad,

thanks for your image. I got your response via mail, but it´s not showing up on the thread here. I will try out the constants and report back here.

Kind regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Brad_C
Contributor

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

I wouldn't do that. The reason I deleted the post is the russian translation indicates that is an incorrectly configured device.

It might work, it might not. Having said that, you won't do any damage, it'll just give poor runtime and have issues with the immediate battery reading as it transfers to battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

Hi Brad,

I got in touch with someone who had a working UPS like mine and shared me the correct values.

If someone ever need these, here is a screenshot:

aDoD5LJkcAlZvnFuYCNKYg%3D%3D.pngaDoD5LJkcAlZvnFuYCNKYg%3D%3D.png

Thanks for all the help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Brad_C
Contributor

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

Are you *sure* that's an SUA? The firmware code looks more like a 3rd generation SU.

With a manufacture date of 2001 it's be in a gray area.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

0 Likes
0
4779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:37 AM . Last Modified: ‎2024-03-17 11:12 PM

On 1/31/2019 4:15 AM, Brad said:

Are you *sure* that's an SUA? The firmware code looks more like a 3rd generation SU.

With a manufacture date of 2001 it's be in a gray area.

The UPS I got the values from are exact the same model.

The manufacturing date is not real, just something I´ve put in temporarily until I´ll figure out the real one. Same goes for the battery replacement date.

Reply

Link copied. Please paste this link to share this article on your social media post.

aycontrerasss
aycontrerasss
Explorer

Posted: ‎2025-11-02 06:47 PM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-02 06:47 PM

Hola,por favor me puedes indicar como hicistes para lograr colocar el modelo y los valores de voltaje,tengo un problema con un surt6000xlt que no me indica el modelo y los valores de voltaje no me deja cambiarlos

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore