ATS AP4450 doesn't deliver power when switched to source B

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ATS AP4450 doesn't deliver power when switched to source B
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
dnll
Crewman dnll
Crewman

Posted: ‎2024-03-12 06:13 PM

0 Likes
3
864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-12 06:13 PM

ATS AP4450 doesn't deliver power when switched to source B

Title. When on source A, power is delivered to all outlets, but when on source B, no power is delivered to the outlets. The ATS is on in either case, I can connect to the NMC just fine and don't see any errors or anything. I tried swapping the sources from the 2 different circuits and it's always source B that is problematic no matter where it's plugged in.

 

Any insight on what/where to look for would be appreciated.

  • Tags:
  • 4450
  • ap
  • apc
  • ats
  • pdu
  • power
  • source
  • switch
  • transfer
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Janeway Teken
Janeway

Posted: ‎2024-03-14 08:14 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-14 08:14 AM

A couple of questions come to mind as to the operational state of the ATS. 

LCD: What does the LCD indicate as to the voltage & frequency? Both should display 120 VAC / 60 Hz. If not you have to identify where the input fault is such as at the outlet, power cord, internal ATS PSU.

 

LED: When the ATS is transferred to source B. Does the LED show the normal flow of power?

 

Transfer: When you press the front A, B, AB source button does it work and is there a sound when engaged? There will always be a very distinct (thunk) sound when the primary source is selected.

 

Logs: What does the error logs show in terms of errors, line condition, operational status? Anytime you unplug a source input the logs will declare a fault and unsync state.

 

NMS: If this unit is monitored by a Network Monitoring System (NMS) it should indicate the DC power supply voltage, hardware state, etc. What are they as this will narrow down the issues.

 

At the most basic level if the ATS was unplugged. As soon as you apply power to any input plug there will be a distinct (thunk) indicating power is applied and the relays are engaged. If you do not hear any sound when power is applied to (Source A / B) there is an obvious electrical / mechanical fault.

 

If you do hear the thunk sound this indicates the ATS does see input power. So the next step is to determine if the electrical circuit is operating as expected. 

As noted up above the front panel has a manual button to select between the sources. If this doesn’t work you have narrowed down the problem as the selector. That can be the button is faulty so you can use the web interface to select the source.

 

If the web interface also doesn’t allow the source to be selected you’ve isolated to the control system. If however the ATS does allow you to change the source you should see and hear that change. If you don’t hear anything but the face and UI show a change of source.

 

You have narrowed the problem to a hardware issue which normally indicates failed relays.

 

These relays can be replaced by a qualified repair facility without too much hassle.

 

Let me know what you observe! 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lieutenant dpierce4776
Lieutenant

Posted: ‎2024-03-15 03:14 PM

0 Likes
0
836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-15 03:14 PM

I have run into a similar issue with the AP77xx line. Mainly in the 120 volt series as the AP4450 is. After talking with tech support and some testing and trouble shooting with electrical engineers on units giving issue. This is what I have found.

 

The switching mechanism that switches between input A and input B on the ATS is two pieces of metal each attached to the hot and neutral output wires, that are attached to an electromagnet. The way it is supposed to work is unit powers the electromagnet in a negative charge with the desired selected input charged positive first and then charges the secondary side up. This is why as @Teken said you should hear a "Thump" when one side loses power for whatever reason. the magnetic forces attract each other since the primary side as now lost its charge the now only positive charged side pulls the negatively charged switching mechanism to it. When power is restored to the primary side the ATS monitors the power from that side then positively charges that side and removes the charge from the other sides electromagnet to make the switching mechanism stich back to that side.

I say all that to say this I have seen times that:

1. In a quick power flicker the switching mechanism gets stuck in the middle and no power is going to the output of the ATS.

2. The programing of the ATS gets "confused" for lack of a better term and does not de-energize one side causing switching mechanism to be "stuck" to one side so long as the ATS has any power to it.

3. in some (very rare) cases if dirt or debris gets in or there is a lot of power flickering or surges the switching mechanism can melt or hot and become welded to one side of the input.

You can try doing this to resolve your issue if either #1 or #2 are the case which 99.9% of the time with issues like yours. Remove power from both inputs to the ATS. wait at least 30 seconds to 1 minute for the ATS and its capacitors to completely drain their charge. That also drains the electromagnet of its charge. Then plug in the side that was not working before. If that works then try plugging in the other input to the ATS and see if it will switch to that side as well as back and forth. Remember just selecting a "primary" side will not be instantaneous. It will take a few seconds to switch, as the ATS makes sure that power is "OK". But if you pull the power cord out of its power source it should be instantaneous as no "checking" is done then. Although I do not recommend that method.

If the ATS still does not output power from the B side then it is most likely welded and you need to replace it

Reply

Link copied. Please paste this link to share this article on your social media post.

dnll
Crewman dnll
Crewman

Posted: ‎2024-03-16 06:33 PM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-16 06:33 PM

Thank you for your help. Since I have 2 units (one of them working perfectly) I should be able to hear the difference about the "thump". I will comment back once I have time to do some additional testing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of