Hi,
I've been asked to enable https on some APC7723 units, they are all in production and on critical systems. I read in the manual that "When you enable SSL, you must reboot the Automatic Transfer Switch".
Does this restart apply to the network management card only, or will the ATS will drop power? 😧
In other parts of the user guide the Network Management Card is usually specifically referenced, not the ATS itself.
Any clarification would be greatly appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:25 PM . Last Modified: 2024-01-31 03:01 AM
Hi,
When you add HTTPS to the network interface of the AP7723 you reboot the network interface only. the ATS remains on line.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:25 PM . Last Modified: 2024-01-31 03:01 AM
Hi,
When you add HTTPS to the network interface of the AP7723 you reboot the network interface only. the ATS remains on line.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:25 PM . Last Modified: 2024-02-14 10:13 PM
Thanks Bill