APC UPS 200XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC UPS 200XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
121
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
11
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

APC UPS 200XL

Please guys,

I have this APC UPS 200XL that keeps showing overload and long beep with no load on it. This actually started after I fixed the initial issue (blowing any mosphet installed in it) it was having.

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

Yes I've gotten a usb to serial converter and I've also gotten a powerchute cable using the diagram you sent, but its still not seeing the ups using pcbe agent

The cable i got, when I plug it to the ups when powered on it switches from source to battery and the battery graph indicates 2 bars. I don't know if that's how it works.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 11
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

I replied in your other thread. Did you look at any of the things I suggested?

- Mosfet driver waveforms

- UPS configuration via serial console

- Acoustically identify source of high pitched sound

Check pin 6 of the ADC0838. That's the scaled voltage from the output power sensing circuit. It is scaled in hardware between 0 & 5V. That reports as power using the serial console, and it relies on the power scaling calibration constant in the uC being correct, which is why I suggested you look at the UPS configuration in the serial console. If the constant is screwed up it can lead the UPS to report high power when there is little to no load applied.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

I've not been able to check the drivers waveform and the serial console. But I checked the pin 6 of ADCADC0838 its producing 36v sending same 36v through D30 while D30 is producing the normal 5v from the other end which is getting me confused.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

On 1/9/2017 7:10 PM, Samuel said:

But I checked the pin 6 of ADCADC0838 its producing 36v sending same 36v through D30 while D30 is producing the normal 5v from the other end which is getting me confused.

Something is terribly wrong with your measurement setup. Pin 6 of the ADC0838 is an input. It produces nothing. The voltage is sourced by pin 1 of IC8 (TL064 Op Amp) and that has a -8V to +12V supply. That output is clamped to a maximum of 5V By D30 and divided *down* by R87 & R88 before it hits the input (pin 6) of the A/D converter. If you are measuring 36V on one side of D30 and 5V on the other side there is something catastrophically wrong with your meter or your methodology.

Try using Pins 9, 10 or 11 on the ADC0838 as your ground reference and measure pin 6 again.

Before you dive back in with a meter, beg, borrow, steal or make a serial console cable and ask the UPS itself what it is seeing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

Thanks Brad.

The serial cable I have is not communicating between the ups and my system ill be pleased if you can help me with diagram on how to convert one end of my serial cable to usb.

More so, I discovered that the problem is actually with IC17 which has link with the transformer. I changed it and the sharp noise stopped and everything became OK. It worked well (with the transformers of the SU3000)on battery without the overload signal. But when i connected it to work online, it flashed the mosphets and started behaving like that SU3000 that I sent you a video on how it was behaving.

Its obvious that the transformer of the SU3000 is what's disturbing the boards. But I've resolved at working on the board and use another transformer with it. Meanwhile, I still need a diagram on how to connect serial cable with my laptop using usb on the other end as my laptop is not having the serial port.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

Its a normal APC UPS with serial number; GS0036000278 and model SU2200XL

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

Serial cable :

http://networkupstools.org/protocols/apcsmart.html

USB to Serial converter :

http://www.ebay.com.au/itm/Com-Port-Serial-Convert-Adapter-Ch340g-Usb-2-0-To-9-Pin-Rs232-Ic-New-L-/2...

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

Thanks Brad, I've place an order for it though not with eBay but with a local online store (Konga) as I don't have a dollar account to make purchase from eBay. 

I'll give you feedback as soon as I get the cable though I'll still try the initial one you sent.

Thanks a lot, you've been of help immensely. I sincerely appreciate. With people like you and aa forum of such, I can boast of using and fixing APC UPS.

You guys are wow!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

Pretty much *any* USB to serial converter/cable will do the job as long as you put the APC "smart" cable on the end of it. You don't need to wire up any of the control lines, GND, Tx & Rx are all you need to talk to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

That smart cable is where the problem lies, as getting it is always difficult.

I have one normal printer USB that I've tried severally but its not communicating with my ups. Could it be compatibility issue? I was actually thinking with the serial to usb converter, any usb cable will work it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

On 4/9/2017 11:31 PM, Samuel said:

That smart cable is where the problem lies, as getting it is always difficult.

Which is why I pointed you at a diagram that shows how to make one. Have you done that?

On 4/9/2017 11:31 PM, Samuel said:

I have one normal printer USB that I've tried severally but its not communicating with my ups.

I don't know what a "normal printer USB" is. I certainly haven't seen a printer with an RS232 port for a few years now.

On 4/9/2017 11:31 PM, Samuel said:

I was actually thinking with the serial to usb converter, any usb cable will work it.

Have you got a USB to Serial converter, and have you put an APC Smart cable between that and the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-18 01:28 AM

Yes I've gotten a usb to serial converter and I've also gotten a powerchute cable using the diagram you sent, but its still not seeing the ups using pcbe agent

The cable i got, when I plug it to the ups when powered on it switches from source to battery and the battery graph indicates 2 bars. I don't know if that's how it works.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of