APC Symmetra LX 16000 (SYA8K16PXR) - Phase L1 and L2 - spread load to increase Runtime?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2908:17 AM. Last Modified: 2024-03-1203:09 AM
APC Symmetra LX 16000 (SYA8K16PXR) - Phase L1 and L2 - spread load to increase Runtime?
We have a Symmetra LX 16000 (SYA8K16PXR), with nine SYTB5 batteries (each less than a year old) in the XR1 rack, and three 4kVA power modules, but have the following Power Draw status (see image below).
Would we get better Runtime if the load was better distributed across the Phase L1 and Phase L2 ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2908:17 AM. Last Modified: 2024-03-1203:09 AM
I don't think you'll get better runtime but you'd be less likely to overload the UPS in the event of a Power Module Failure. General load balancing principles should apply here though - you want to have approximately equal load on phases throughout the facility.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2908:17 AM. Last Modified: 2024-03-1203:09 AM
I don't think you'll get better runtime but you'd be less likely to overload the UPS in the event of a Power Module Failure. General load balancing principles should apply here though - you want to have approximately equal load on phases throughout the facility.