APC Smart-UPS and BS7671/BS7909 disconnection times

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS and BS7671/BS7909 disconnection times
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
dimitrisb
dimitrisb
Cadet

Posted: ‎2025-04-22 09:14 AM

0 Likes
4
205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-22 09:14 AM

APC Smart-UPS and BS7671/BS7909 disconnection times

hi

What would be the Automatic Disconnection Time for a short circuit fault on the load side of an APC UPS?

In the scenario that there is a L/N short on the load side of the UPS, the breaker feeding the UPS will trip but then the UPS battery power will kick in right? So the UPS will see the short as an overload and turn itself off.

 

Would that meet the requirements of SC disconnection times of 0.4s?

 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Janeway Teken
Janeway

Posted: ‎2025-04-23 05:07 AM

0 Likes
3
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-23 05:07 AM

That depends upon many factors such as the type of failure mode and the amount of current flow. 

The two most common failure modes are a slow & random partial short. The other is a catastrophic and immediate dead short.

 

This than comes down to how sensitive the UPS output circuit is and how fast the relays are designed to react.

 

Only a validation test can determine how a specific unit will behave. Keep in mind presenting a dead short on the output can and may cause the unit to fail! ☝️

 

As such, using a regulated power supply to limit the maximum amount of current draw is imperative. 

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

dimitrisb
dimitrisb
Cadet

Posted: ‎2025-04-24 12:33 AM

In response to Teken
0 Likes
2
128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 12:33 AM

Thanks for the reply. 

The reason I'm asking is because I work for a hire company for events and we need to comply with the regulations set by BS7909 which require Automatic Disconnection Times on final circuits of <400ms for L-N Short and <300ms for Earth Fault.

Earth Fault is not as much of an issue as with an RCD we only need about 30mA of Prospective Fault Current and the UPS being a floating supply when on battery mode.

 

The issue is with L-N short. We will have to measure the Prospective Short-Circuit Current at the final circuit and make sure that the protective device will disconnect at <400ms.

Say we get 300A of PSC measured at the female end of the appliance lead feeding a unit connected to the UPS.

If there is a L-N short on that unit/appliance lead and the UPS is on utility then no problem, the C16 MCB/RCBO feeding the UPS will disconnect in <400ms.

The issue is that then, the UPS will kick in due to loss of supply. Will the battery mode UPS, in turn and presented with a short and 300A, disconnect within 400ms to meet BS7909 requirements?

 

We could get around the issue by placing an MCB inline on the UPS outputs. Then we will need to know what the MAX current flow of the inverter would be so we can select an appropriate curve/rating MCB to achieve ADT of <400ms. If for example we know that max overcurrent of the UPS is 20A we would have to install a B4 MCB on the outs to meet BS7909 requirements.

 

So I'm guessing the manufacturer should be able to provide this information? Or as you said we will have to experiment!

Specifically I am referring to our hire stock UPSs

APC SMC1500I-2UC

APC SMT750RMI2U

 

And the older

SUA1500RMI2U

 

Thanks for any advice!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2025-04-24 08:37 AM

In response to dimitrisb
0 Likes
1
125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 08:37 AM

You may review this APC FAQ as it relates to Short Circuit on specific models and the stated behaviour:

 

https://www.apc.com/us/en/faqs/FAQ000247935/

 

I suggest you reach out to APC Technical Support for any relevant technical information pertaining to short circuit protection.

 

More specifically the *White Paper* that discusses how APC addresses this issue. As the support guy will probably have no idea besides referencing the external breaker / internal fuse rating. 

Keep in mind a UPS by its very design uses a slow b-low fuse / slow reaction breaker. 

There are no GFCI rated (output) UPS’s in the Enterprise market due to its inherent use case and intended purpose. 

Lastly, if there is a short detected on the output the system will call this out. How the system reacts is determined by the design topology and the type of short presented to the system.

 

You’ll find that some units do nothing besides alert you of a output short. Whereas others will terminate the output voltage upon detecting a short.

 

Again, this varies from model to model and firmware installed on the system.


Lastly, do not assume using a resistive load is the same vs a reactive one when validating a system under test. ☝️

 

Regardless of all the above a solid low resistance single point Earth ground is essential for equipment and human safety. 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

dimitrisb
dimitrisb
Cadet

Posted: ‎2025-04-24 04:35 PM

In response to Teken
0 Likes
0
92
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 04:35 PM

Thank you so much for all the advice!

 

 

IF it's slowb-low type fuse/breaker on the UPS then I'm guessing an MCB on the outlet of the UPS would react before the UPS had any chance to react if presented with a L-N short as an MCB would trip in less than 100ms all the way down to 5-10ms.

 

Will do further enquiries.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of