APC Smart-UPS RT 3000 (SURT3000) - 20W Charge Rate & 93V Reading after Manual Calibration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS RT 3000 (SURT3000) - 20W Charge Rate & 93V Reading after Manual Calibration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Aka1ca
Aka1ca
Cadet

Posted: ‎2025-12-03 08:33 AM . Last Modified: ‎2025-12-03 08:49 AM

0 Likes
9
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-03 08:33 AM . Last Modified: ‎2025-12-03 08:49 AM

APC Smart-UPS RT 3000 (SURT3000) - 20W Charge Rate & 93V Reading after Manual Calibration

Hi everyone,

I have an APC Smart-UPS RT 3000 (SURT3000) and I am looking for confirmation on its charging behavior.

Current Setup:

  • Model: SURT3000 (192V Battery System)

  • Batteries: Brand new, installed yesterday.

  • Action: I performed a manual runtime calibration with a 600W load. The unit ran for 45 minutes before shutdown, confirming the batteries are healthy.

The Issue: After the calibration, I plugged the unit back into mains power. The unit is currently functioning and online.

However, monitoring the unit via software shows two confusing values:

  1. Charge Power: It is steady at 20 Watts.

  2. Battery Voltage: It is reporting 92.92 V.

My Questions:

  1. Regarding the 20W: Is this a normal "Soft Start" or trickle charge mode because the batteries were drained? At what voltage will it switch to full bulk charging?

  2. Regarding the 93V: Since this is a 192V system, is the software reading just half the DC bus (Positive-to-Neutral)? If the total DC voltage were truly 93V, I assume the unit wouldn't be able to stay Online.

I just want to make sure the charger isn't faulted before I leave it alone for 24 hours.

Thanks for any advice!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Next Topic
Replies 9
Aka1ca
Aka1ca
Cadet

Posted: ‎2025-12-04 02:16 AM

0 Likes
8
167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-04 02:16 AM

The batteries are 11.6v each. Maybe the batteries discharged too low and the charger won't accept to charge ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-12-04 03:17 AM . Last Modified: ‎2025-12-04 03:18 AM

In response to Aka1ca
0 Likes
7
162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-04 03:17 AM . Last Modified: ‎2025-12-04 03:18 AM

Is the voltage increasing now along with the battery capacity since you last wrote?!?!

 

Provide a screen capture of what you’re seeing along with the event, and data logs.

 

The specifications indicate the unit incorporates a 382 watt charging system.


Keeping in mind the system is temperature compensated as such the charging / float voltage will fluctuate based on the internal temperature seen by the system within the RBC compartment.

 

Im not sure why you performed a out of band battery calibration vs using Power Chute / NMC?!?!

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Aka1ca
Aka1ca
Cadet

Posted: ‎2025-12-04 03:38 AM

In response to Teken
0 Likes
6
158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-04 03:38 AM

Hi, thank you for your reply.

​I performed a manual calibration because I did not have access to a laptop/software at the time. The batteries are brand new, and during the test, they successfully held a 600W load for 45–50 minutes, so I know the cells are healthy.

​However, now that I have plugged it back in, it seems like the charger isn't working. It appears to be slowly draining the batteries rather than charging them, even though the UPS is connected to wall power.

​Current Status:

  • ​LEDs: The 'Online' light is solid green, but the bottom battery indicator is flashing. There are no error lights.
  • ​Voltage: When I measure with a multimeter while it's plugged in, the voltage is slowly dropping.
  • ​Battery Level: The batteries are currently sitting at around 11.6V per block (deeply discharged).

​Is it possible that the voltage is simply too low for the charger to activate? Does the charging circuit fail to recognize batteries when they are discharged this deeply?"

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-12-04 04:44 AM

In response to Aka1ca
0 Likes
5
151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-04 04:44 AM

Yes, the RBC must be at a minimum level or (SOC) State of Charge. 

I would suggest you remove the RBC and disconnect all the cells and manually charge all the cells.

 

Once fully charged reconfigure and insert the RBC into the system.

 

NOTE: It’s critical to understand when the RBC is replaced the following steps be completed in sequence:

 

Date: The battery installation date must be updated if available via the following methods if present: LCD, NMC, Power Chute.

 

Doing so resets internal counters and adjusts charging tables if applicable. 

Self Test: Manually initiate a self test and let pass. Wait for the RBC to return to 100% SOC.

 

Calibration: Manually initiate the battery calibration with a minimum of 30% load or greater via the following methods if available: LCD, NMC, Power Chute.

 

Allow the RBC to recover back to 100% SOC. This procedure will help the system learn the battery health and better reflect the operational runtime via LCD, LED, NMC, Power Chute, APCUPSD, NUT.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Aka1ca
Aka1ca
Cadet

Posted: ‎2025-12-04 05:13 AM

In response to Teken
0 Likes
4
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-04 05:13 AM

Thanks for the detailed advice.

Since I do not have a dedicated lead-acid battery charger available, can I use a variable DC Bench Power Supply to charge the cells individually?

If this is safe, I have two questions:

  1. What are the recommended Voltage (CV) and Current/Amperage (CC) limits to use on the power supply for safe charging?

  2. Do the batteries need to be manually charged all the way to 100%, or is it sufficient to bring them up to a specific threshold (e.g., 12.3V – 12.5V) just so the UPS charger can detect them and resume normal operation?

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-12-05 12:11 AM

In response to Aka1ca
0 Likes
3
90
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-05 12:11 AM

1. Charging voltage can range from 14.4 ~ 15 VDC. Float voltage can range from 13.5 ~ 13.8 VDC. 2.7 Amps is the maximum per cell.

 

2. Ideally the cell s hould be fully charged to 12.8 ~ 12.9 VDC. But, you can bring the cells to at least 12.6 VDC to play it safe.

 

Given there are 16 cells in each RBC X 2 for a total of 32 cells. I would parallel as many cells together you feel comfortable with to charge.

 

Four cells in parallel would be a good compromise.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Aka1ca
Aka1ca
Cadet

Posted: ‎2025-12-05 09:29 AM

In response to Teken
0 Likes
0
5
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-05 09:29 AM

I will try, will keep update here

 

Thank you 

Reply

Link copied. Please paste this link to share this article on your social media post.

Aka1ca
Aka1ca
Cadet

Posted: ‎2025-12-05 12:47 PM

In response to Teken
0 Likes
1
5
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-05 12:47 PM

I have an update regarding my battery issue.

Since the batteries were deeply discharged, I removed them and manually charged each battery individually to 12.0V using an external power supply. The total string voltage is now nominally 192V.

The Current Behavior:

When I reassembled the pack and turned the UPS on:

The Charge Power spikes to 180 W for a brief moment.

Immediately after that, it drops down to 20 W and stays there.

The Battery Voltage appears to be slowly dropping instead of rising (likely due to the internal load of the UPS fans/logic being higher than the 20W charge).

On the front panel, 2 Battery LEDs are lit solid green.

My Question:

Is 12.0V per battery still too low for the main charger to engage fully? Do I need to take them out again and charge them higher (e.g. to 12.5V or 12.8V), or does this "180W to 20W" drop indicate a different issue with the charging logic?

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-12-08 03:39 AM . Last Modified: ‎2025-12-08 03:40 AM

In response to Aka1ca
0 Likes
0
0
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-08 03:39 AM . Last Modified: ‎2025-12-08 03:40 AM

As stated the RBC must be at a minimum 12.5 ~ 12.6 VDC otherwise you’re just wasting time. 

 

At this point I would highly suggest you complete a brain dead reset to clear any soft faults / errors before you move forward:

 

https://www.se.com/ca/en/faqs/FA156611/

 

Once the above procedure has been completed measure the output voltage from the UPS RBC connector and report the DC voltage. 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore