APC SUA3000I FAIL. LED FLASHING SEQUENTALLY. THE EEPROM IS FAIL?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SUA3000I FAIL. LED FLASHING SEQUENTALLY. THE EEPROM IS FAIL?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:53 PM . Last Modified: ‎2024-03-07 01:47 AM

0 Likes
4
1412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:53 PM . Last Modified: ‎2024-03-07 01:47 AM

APC SUA3000I FAIL. LED FLASHING SEQUENTALLY. THE EEPROM IS FAIL?

Help me with this UPS

The ups is not connected to the powerchute. is not connected to any computer

 

Case 1:

When I connect the main power the UPS works ok.

When I switch it to battery mode, the UPS has normal voltage output. After 1 minute with 30 seconds (approximately) the UPS cuts the output voltage and the lights flash sequentially, reconnect the main power supply and switch to line mode in a normal way.

Case 2:

I connect the main power the ups works ok.

I remove the main power and the UPS is put in battery mode (So far so good) after 5 seconds reconect the main power, the ups goes to online mode, after 1minute 25 seconds the ups short output voltage and flashes the lights sequentially, and return to line mode.

Conclusion:

The UPS when entering battery mode after 1 minute 30 seconds regardless of whether it reconnects or not reconnects the main power (Ac input) cuts its output voltage.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:54 PM . Last Modified: ‎2024-03-07 01:47 AM

0 Likes
0
1412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:54 PM . Last Modified: ‎2024-03-07 01:47 AM

Do you think it is an error of the EEPROM or the Microcontroller? I have noticed that the pulse that deactivates the output comes from the microcontroller.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:53 PM . Last Modified: ‎2024-03-07 01:47 AM

0 Likes
0
1412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:53 PM . Last Modified: ‎2024-03-07 01:47 AM

Hi Luis - 

When you say Sequentially, so you mean that they are scrolling top to bottom? This would indicate that the UPS has exhausted its battery power and has gone to sleep mode. What % of load is connected to the UPS? How old are the batteries?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:53 PM . Last Modified: ‎2024-03-07 01:47 AM

0 Likes
0
1412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:53 PM . Last Modified: ‎2024-03-07 01:47 AM

The batteries are in good condition. They're new.
Better I leave you the video so you can observe better.
It has no connected load.

This is a video that I recorded of the UPS.

If you like, You can see the whole process. The fault stars at 1:35 of the video.

The link of  my  video: https://www.youtube.com/watch?v=82snNZfhPSw

Here is another video that I found on the Internet: https://www.youtube.com/watch?v=voFGnzbQuCE

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:54 PM . Last Modified: ‎2024-03-07 01:47 AM

0 Likes
0
1412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:54 PM . Last Modified: ‎2024-03-07 01:47 AM

There is definitely a problem with the UPS. Those indicators would normally mean that the unit had gone to sleep after depleting the batteries. In your case it looks like the unit goes to that state for just a single cycle, drops the load, and comes back online. This is definitely not normal behavior. I would reccommend replacing the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:54 PM . Last Modified: ‎2024-03-07 01:47 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:54 PM . Last Modified: ‎2024-03-07 01:47 AM

Do you think it is an error of the EEPROM or the Microcontroller? I have noticed that the pulse that deactivates the output comes from the microcontroller.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore