Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

APC SRV3KI error 0uF 114

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: APC SRV3KI error 0uF 114
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:37 AM

0 Likes
13
14758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:37 AM

APC SRV3KI error 0uF 114

Hi

UPS is on bypass mode due to fault, the error display was "0uF 114" i cant find the code in the user manual. Maybe, anyone knows what error is this. 

Thanks

Labels
  • Labels:
  • General Questions & Suggestions
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
4
14733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

This can be resolved with a firmware update:

How to:

http://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/416000/FA4160...

Firmware:

http://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/416000/FA4160...

-Gavan

See Answer In Context

  • Tags:
  • Hola buenos días trato de descargar firmware con este link no me deja me sale en mantenimiento la pagina hay otro link
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Fureisenjin_apc
Fureisenjin_apc
Cadet

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
0
14733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

Hello did your issue get resolved. I got the same issue yesterday with one of our APC SRV3KI.

 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
0
14733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

Nope, i already claimed for warranty ( for the 2nd time ). Hard reset will temporary solve the issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
4
14734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

This can be resolved with a firmware update:

How to:

http://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/416000/FA4160...

Firmware:

http://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/416000/FA4160...

-Gavan

  • Tags:
  • Hola buenos días trato de descargar firmware con este link no me deja me sale en mantenimiento la pagina hay otro link
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
0
14734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

Hi 

Thanks I'll try this, hopefully is work. Give you update soon.

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
0
14734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

Hi Gavan

Just for the update, during firmware update a error was encountered. kindly see the attach screenshot. After few retry..update was successful from version 0.9 to 1.0. Hopefully the 0uF error will no longer be a issue.

0uF 114 error what is this all about?

 

 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
0
14734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

Sorry I'm not on the UPS hardware-side so I don't have any details on the issue I just know the update was released to fix it.

- Gavan

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

0 Likes
0
14734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:02 AM . Last Modified: ‎2024-03-19 02:36 AM

ah okies no worries, last thing, is firmware update is applicable to all SRV Model ( 1KVA to 10KVA )with 0uF Error?

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Alikabir84
Alikabir84
Cadet

Posted: ‎2022-04-02 10:57 AM

In response to BillP
0 Likes
0
13432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-02 10:57 AM

I have a SRV1KI and recently I got his error too, In my case I bought a new power supply to upgrade my system going from a 850 watts to 1000 watts power supply  system usage is well under 420 watts at load maximum. So when I tried to boot from this new corsair RM1000x supply the APC SRV1KI went into Bypass mode ( for the first time) and would not shutoff I had to press the main button for a few seconds to reset. Its been working fine with my OLD 850 watts supply which is also Corsair RM850x. LED display showed 0uF and code was 114? what is this code and why is the ups acting up when I trying to boot from a new supply while old one works, its only an increment of 150 watts and the load is not even applied. Also did this when "only the supply was connected without any equipment attached". 

 

Is this Firmware necessary for this fix? what really is this 114 code , it said on top to check manual and there isn't any information about it in the manual.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Abimanyoo21
Abimanyoo21
Cadet

Posted: ‎2022-05-04 05:59 PM

In response to BillP
0 Likes
0
13053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-04 05:59 PM

Hi. I'm not able to open the link given. Is there any other way or any other links?

@BillP @Anonymous user 

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

blacAces_apc
Crewman blacAces_apc
Crewman

Posted: ‎2023-04-19 07:53 PM

1 Like
0
9593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-19 07:53 PM

Hi @BillP  is there any chances i can adjust the Contrast of the LCD Display for SRV? As of now its too hard to read the display. No instruction in the user manual.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

mohamed2023
mohamed2023
Cadet

Posted: ‎2023-11-10 04:30 PM

0 Likes
0
7189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-10 04:30 PM

Go to the settings menu and adjust the output from 230 to 220 or vice versa according to your input voltage and restart the device. Error 114 and 116 out

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Poulomi
Poulomi
Cadet

Posted: ‎2024-06-24 05:08 AM

In response to BillP
0 Likes
1
4803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 05:08 AM

These links are no longer working....

Got the same issue yesterday with SRV3KI-TW

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

leang97
leang97
Cadet

Posted: ‎2024-09-11 11:34 PM

In response to Poulomi
1 Like
0
3679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-11 11:34 PM

I thought this would help. I encountered this problem around a year ago.
My SRV3KI would beep "Battery BDC" <bDC> from time to time and would resolve itself automatically waiting 10 minutes. But there is an "FAQ" page that gives gives us an update to this <bDC> issue

The said links : - 
Easy-UPS reports bDC <Battery Disconnected> | Schneider Electric Philippines (se.com)

But after updating to this firmware, my SRV3KI experienced a more serious problem stating error 0uF 114 randomly with all protection OFF. Nothing can do until SRV3KI restarts, and it would 0uF 114 randomly again next time. 

So I found this post, and downloaded this file before the links are dead, and it fixes the 0uF 114 error, and so far no more random <bDC> problems. For those who seek for the file, luckily I have backup, if I was right, the firmware will update SRV3KI into firmware version 1.0 "36-002287-06s1". 

Btw, just my advice, if something is going wrong with your UPS, take it to authorized service center to check. 

I attached the file again for somebody who needs it.

Attachments
Easy UPS Online Firmware File and Software.7z
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of