Hi
I have an APC SMT750RMI2U UPS that is working fine, until I connect it to the network with a CAT5 cable.
As soon as I do this, about 5 seconds later it shuts down with a message "Output off by Software"
I had a look in Powerchute (connected it with a USB cable) and can't see any relevant settings or anything on the logs.
I tried disconnecting and reconnecting the battery but it didn't solve the issue.
Any help much appreciated
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-05-20 05:37 AM
Show me a photo of the rear of the system and where you connected the CAT5 RJ45 Ethernet cable.
If you connected your CAT5 Ethernet cable to RJ50 Serial Ethernet port on the rear of the UPS frame .
That’s why it shut down because that specific port uses a proprietary (internally wired) serial cable.
If you connected your CAT5 Ethernet cable to a NMC. Show me all the output power settings.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-05-20 05:37 AM
Show me a photo of the rear of the system and where you connected the CAT5 RJ45 Ethernet cable.
If you connected your CAT5 Ethernet cable to RJ50 Serial Ethernet port on the rear of the UPS frame .
That’s why it shut down because that specific port uses a proprietary (internally wired) serial cable.
If you connected your CAT5 Ethernet cable to a NMC. Show me all the output power settings.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-05-21 12:58 AM
Hi there
Thank you! I think you solved it
I was connecting the network cable to the "serial" RJ45 port.
We have some UPSs that don't have a Network port so I got confused.
Solved!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-05-21 06:06 AM
Appreciate you confirming the root cause so please do mark my previous reply as a solution.
So it may help the next person asking the same.
Rock On . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of