Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC AP7921 ATS Failure or...?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC AP7921 ATS Failure or...?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:02 AM . Last Modified: ‎2024-02-14 11:14 PM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:02 AM . Last Modified: ‎2024-02-14 11:14 PM

APC AP7921 ATS Failure or...?

In the past couple of weeks I experienced a mains power failure, which had some unexpected impact at the time which I have started looking further into.

My setup is the following:

1. Mains feed directly running into SourceA on my ATS
2. Mains feed also running into my APC SMT1000I UPS which feeds SourceB on my ATS

The idea is that I can run on mains power OR UPS, and have one or the other supplying power.  This also allows me to take the UPS out of service if required.

The total loss of mains power event two weeks ago caused all devices on the ATS (router, switch, wireless controller and a server) to fully power cycle also.  I suspect this may have been because I didn't have the ATS set to "High" sensitivity.  So I have since rectified this.  The frequency deviation is set to 3Hz now but that made no difference.

However since making this change my ATS is frequently (every 2 hours or so) going into a "spasm" state where for anything between 2 - 10 seconds it fails over between SourceA and SourceB in very rapid succession.  It sometimes switches between A and B 20 or so times during this window and makes noisy clicking sounds and then comes good.  Fortunately during this period the devices connected all stay online.  But it's not a happy type of noise.

Mains power here in NSW Australia is overall very good.  We usually have less than 1 outage each year and the data from the ATS shows a very stable 240 +/- 3 volts with 50Hz +/1 1 for very long periods of time.  Now I could almost accept if the unit occasionally switched away from mains power, but it's switching to and from UPS feed which makes me think it's the unit and not the supply which is the cause.

I have power cycled the ATS but this made no difference.  The ATS is under 2 years old and was bought new, but the serial number lookup tells me that the UPS serial number can't be found (it's an ATS...).

Firmware is the latest - and yes when I upgraded it I followed the instructions about having only feed A actually supplying.

Where do I go next with this?  Has anyone else experienced this before?

Thanks,
Reuben

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7721
  • ats
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore