Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC 9302 Console Port Server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 9302 Console Port Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
4
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

APC 9302 Console Port Server

Hello,everybody!
Have problem with CPS APC 9302(last firmaware)
Configured as follows-security profile-Open,all network configures done,port profile-9600 8N1 DCD-Disregarded.
I tried to connect it to several Sun servers and workstations (Netra T1,Ultra 5,V250) with patch cord and cross cable.
But none works,neither through java applet or ts_menu command.
Tried to connect with Console (Telnet/Raw) options. With telnet options-everything stops and shows nothing...but message in log-client doesn't support telnet com port protocol option rfc 2217,but Ultra 5 have additional signal DCD,when I put DCD-Regarded,this message in log dessapears. But on other servers all the same.
Please help!!!! need to show OBP to clients,but all servers are on another site.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

thank you very much!!!!))))))
thats really helped.
I thinks while tecnology still in use you should know its history,will work on it!)
Ultra 5 connected and working fine.
Now Iam trying Netra T1 with selfmade RJ45-RJ45 cable.
Thanks again))!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

you need to make sure you are using the correct adapters and cables for your operation..

The following cables and adapters are available for purchase from APC to use with your CPS.
Choose those that are appropriate for the equipment you are managing with the CPS.

Cables

AP9307 DB9F to RJ45 crossover cable
AP9308 DB25M to RJ45 cable
AP9309 DB25F to RJ45 crossover cable
AP9317 RJ45 to RJ12 CPS to Rack PDU cable

Adapters

AP9310 DB25F to RJ45 crossover adapter
AP9311 DB25M to RJ45 crossover adapter
AP9313 DB9F to RJ45 crossover adapter
AP9314 DB9M to RJ45 crossover adapter
AP9315 RJ45 to RJ45 Cisco/SUN adapter
AP9316 CPS Console Port to UPS DB9 adapter

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

ok,I used simple patch cord/cross cable with my Netra T1 because serial LOM port is RJ-45,but still nothing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

Hi, Anton --

Unfortunately you can't just use standard Ethernet patch cable. Serial communications is, sadly, more complicated than that (RS-232 was invented in 1969).

For two serial devices to talk, the following connections have to be made between them:

Transfer (TX) <--> Receive (RX)
Receive (TX) <--> Transfer (RX)
DTR <---> DSR
DSR <---> DTR
Ground <---> Ground
RTS <-----> CTS
CTS <-----> RTS

I'd explain why, but literally it is like 50 years of uninteresting history. So I'll just cut to the chase: you need to get what is commonly called a "rollover" cable. NOT a "crossover" cable. NOT a "patch" cable.

An Ethernet "patch" cable is this:

Pin1 --> Pin 1
Pin2 --> Pin 2
Pin3 --> Pin 3
Pin4 --> Pin 4
Pin5 --> Pin 5
Pin6 --> Pin 6
Pin7 --> Pin 7
Pin8 --> Pin 8

An Ethernet "crossover" cable is this:

Pin1 --> Pin 2
Pin2 --> Pin 1
Pin3 --> Pin 4
Pin4 --> Pin 3
Pin5 --> Pin 6
Pin6 --> Pin 5
Pin7 --> Pin 8
Pin8 --> Pin 7

A "rollover" cable is this:

Pin1 --> Pin 8
Pin2 --> Pin 7
Pin3 --> Pin 6
Pin4 --> Pin 5
Pin5 --> Pin 4
Pin6 --> Pin 3
Pin7 --> Pin 2
Pin8 --> Pin 1

You can get a "rollover" cable a bunch of ways.

a. APC calls it part number: AP9315 RJ45 to RJ45 Cisco/SUN adapter. They charge $20 for it. A great bargain!
b. Find the "rollover" cable that ships with virtually any Cisco router. It's the same thing. It's usually light blue.
c. Crimp one yourself if you have the tools.
d. Buy it online from some guy in China for literally a dollar. (Google: "rj45 cable rollover". Make sure the resulting page specifically states the pinouts as I described above).

You can guess which one I recommend.

Obviously, once you have the right cable. Try again. If no luck, make sure the serial protocol settings on your LOM match that of the console port server. Notably, baud rate, bit rate, etc.; and DON'T FORGET HANDSHAKING / FLOW CONTROL (on/off).

If you found this post useful, I'd appreciate a private email that I can explain how I know such arcane things as what a "rollover" cable is.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:40 AM . Last Modified: ‎2024-03-18 04:13 AM

thank you very much!!!!))))))
thats really helped.
I thinks while tecnology still in use you should know its history,will work on it!)
Ultra 5 connected and working fine.
Now Iam trying Netra T1 with selfmade RJ45-RJ45 cable.
Thanks again))!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore