New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
APC 8865 PDU, Question on phase and bank configuration setup
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-0605:48 PM
APC 8865 PDU, Question on phase and bank configuration setup
Hi all,
Setup is 2 x 8865 pdu's in a rack, Side A and Side B in each rack. Should side A fail all loads will switch to Side B in effect doubling the load of pdu and vise versa.
Current alarm values for each pdu are:
Phase1: 24a, phase2: 24a and phase3: 24a
Bank1: 20a, bank2: 20a and bank3: 20a
The question is, due to the fact of a possible failure on Side A or B and in effect doubling the load on one pdu, what should the values of the phases and banks be set to?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-0709:14 PM
Sorry but I am on my phone and can not see the wiring diagram well.
But typically speaking each bank is fed from 2 phases. Also rule of thumb on breakers is 80% of rating. So the 8865 has a 30 Amp plug so the phase setting should be no higher than 24 amps per phase. The banks should come in slightly lower so your settings are correct.
You should also be balancing the load across phases
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-0804:05 PM
Thank you for the confirmation on the values but what I wanted to actually know is what should the values be if the pdu in question were to take on the load of another identical PDU in case that pdu fails and the load is transferred over.