APC 7901/7920 Rackmount brackets

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 7901/7920 Rackmount brackets
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

0 Likes
10
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

APC 7901/7920 Rackmount brackets

Hi. My company owns an APC 7920 for about two years and now after the purchase of a 42U rack, we would like to rackmount it.

The problem is that the rackmount brackets are nowhere to be found 😞
After contacting APC support, I almost couldn't believe when I was told the rackmounts are not sold separately so they couldn't help (unless I bought a new 7920 I suppose).

Can anyone help? Do you have any rackmount brackets for the 7901/7920 for sale?
Or perhaps do you know any rackmounts compatible or know where I can buy 'universal' ones so I can drill the holes?

Thanks.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM


Hi,

Very sorry about that, didn't mean to mark this particular thread answered, apparently I got a little trigger happy with my search results and the moderator buttons. What country are you in? This forum almost exclusively supports the United States and Canada, so even if we wanted to assist you by shipping you the parts, we could not do so unless you are in one of those two countries. Unfortunately regional support is the only way to get parts shipped for the region/country in question.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

Hi,
We have been looking for this same exact part. I have contacted several resellers and was told that it's discontinued and they can't get it. Is there a new part # or can we get it direct?

Thanks,
Ara

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

0 Likes
0
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

Can't buy it direct unfortunately. What's the model on your PDU? Same as the original poster's?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

Hi. My company owns an APC 7920 for about two years and now after the purchase of a 42U rack, we would like to rackmount it.

The problem is that the rackmount brackets are nowhere to be found 😞
After contacting APC support, I almost couldn't believe when I was told the rackmounts are not sold separately so they couldn't help (unless I bought a new 7920 I suppose).

Can anyone help? Do you have any rackmount brackets for the 7901/7920 for sale?
Or perhaps do you know any rackmounts compatible or know where I can buy 'universal' ones so I can drill the holes?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

If the unit is in warranty we could RMA the brackets to you. The bracket part # is 870-5267. There are no sellable SKUs that I can see that are guaranteed to work with the PDU to be horizontally mounted. You could check for that part # through one of our distribution partners/resellers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:58 AM

Hi.
Thanks for the reply. The unit is not in warranty 😞
Is there any other way I can get that specific bracket?

Regards,
Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

0 Likes
0
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

As I mentioned above, you would need to check through a distributor/reseller for the part. We do have a procedure for sending service parts, but the shipping charge on it would be much, much higher than the actual value of the part. You would need to call into phone tech. support for this option.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

0 Likes
0
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

Assumed answered due to lack of customer update/response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

Why do you assume answered?

What update/response do you want? I still haven't manage to buy a simple pair of rackmounts for this.

Perhaps next time we rearrange our server rooms I'll think twice about APC since we can't even buy a simple pair of rackmounts.

The question is still unanswered and if something is lacking....is customer support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

0 Likes
0
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

Hi.

I've tried different resellers, then I've contacted APC in my country. Response was always the same: 'not available for purchase'.

Then I even contacted APC in the US. Response was 'Sorry....you have to contact APC support in your country'.

In small companies they struggle to sell their stuff to you.
In big companies you struggle to get them to sell to you.

Ridiculous.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:56 AM . Last Modified: β€Ž2024-03-18 03:57 AM


Hi,

Very sorry about that, didn't mean to mark this particular thread answered, apparently I got a little trigger happy with my search results and the moderator buttons. What country are you in? This forum almost exclusively supports the United States and Canada, so even if we wanted to assist you by shipping you the parts, we could not do so unless you are in one of those two countries. Unfortunately regional support is the only way to get parts shipped for the region/country in question.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore