AP9641: after Firmware upgrade regular "UPS: In bypass in response to an internal hardware fault."

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9641: after Firmware upgrade regular "UPS: In bypass in response to an internal hardware fault."
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Hansi98
Crewman Hansi98
Crewman

Posted: ‎2022-06-20 12:10 AM

0 Likes
12
2967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 12:10 AM

AP9641: after Firmware upgrade regular "UPS: In bypass in response to an internal hardware fault."

Hi community,

uI pdated Firmware Smart-UPS SRT1500 AP9641 to 2.2.0.1 yesterday (from 1.4.2.1).

 

Since then (during the last 24hours) I see approx. 40 messages like this:

Code : 0x011B UPS: In bypass in response to an internal hardware fault.

immediately after that:

Code : 0x01B2 UPS: Return from bypass, internal hardware fault no longer present.

 

Serial Number : 5A2053T31151

Device Serial Number : AS2053191323

 

any idea on this issue?

 

There were no previous problem with the device.

are there any links to older firmware version, we might give a try?

 

Is a full power cycle of the UPS recommended to solve this?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-06-20 01:36 AM

0 Likes
10
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 01:36 AM

Hello Hansi

 

 

We have seen a few of these cases and the mitigation is currently to downgrade to the v2.0.0.5 of the firmware.

I have added the v2.0.0.5 firmware to this message, and I suggest using the manual SCP/FTP upgrade process described in this FAQ document -> https://www.apc.com/ie/en/faqs/FA156047/

 

The upgrade and downgrade process is identical in this case.

 

Our software development team is working on the next version of the firmware, that fixes this issue, and it should be incoming before too long.

 

Best regards

Tonny

See Answer In Context

Attachments
apc_hw21_su_2-0-0-5.zip
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-06-20 01:36 AM

0 Likes
10
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 01:36 AM

Hello Hansi

 

 

We have seen a few of these cases and the mitigation is currently to downgrade to the v2.0.0.5 of the firmware.

I have added the v2.0.0.5 firmware to this message, and I suggest using the manual SCP/FTP upgrade process described in this FAQ document -> https://www.apc.com/ie/en/faqs/FA156047/

 

The upgrade and downgrade process is identical in this case.

 

Our software development team is working on the next version of the firmware, that fixes this issue, and it should be incoming before too long.

 

Best regards

Tonny

Attachments
apc_hw21_su_2-0-0-5.zip
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Hansi98
Crewman Hansi98
Crewman

Posted: ‎2022-06-20 02:15 AM

In response to TonKei
0 Likes
9
2952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 02:15 AM

Hi Tonny,

thanks for the quick reply. Just downgraded to 2.0.0.5.

 

BTW: what I observed: This bypass problems occured massively while our network security scanner was checking this device. 

So it might be connected to the CPU/network ultilization of the card.


With 2.0.0.5 i also just ran a security scan (which is checking open ports, trying logons, trying to extract data by SNMP et cetera): no such messages triggered by the scan

Regards


  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-06-20 02:29 AM

In response to Hansi98
0 Likes
8
2948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 02:29 AM

Hello Hansi 

 

Thank you for the feedback.

From what I understand, development has identified the root cause and will implement a fix in the next firmware version.

 

If this resolves the issue for you, please mark the post as solved 😉

 

Best regards

Tonny

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JanKarsten
JanKarsten
Cadet

Posted: ‎2022-06-20 05:24 AM

In response to TonKei
0 Likes
7
2930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 05:24 AM

Hello Tonny, @TonKei 

 

thank you for the information. I face the same issue with 6 of our Smartups with AP9640/41.

 

Do you have any idea, when this fix will be available? 

 

Does this "error" can damage the UPS itself ?

 

Do you suggest to downgrade or is it possible to wait until the fix arrives without having any side-effects?

 

Thank you in advance.

 

Best regards,

Jan Karsten

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KLJ
KLJ
Cadet

Posted: ‎2022-06-20 10:02 PM

0 Likes
0
2906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 10:02 PM

Same error here since I updated 4 AP6940 to v2.2.0.1.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Hansi98
Crewman Hansi98
Crewman

Posted: ‎2022-06-20 10:30 PM

In response to JanKarsten
0 Likes
0
2900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 10:30 PM

Hi  Tonny,

after approx. 18hours of observing: None of these messages appeared again.

So I see this as a workaround until a new firmware >2.2.0.5 is relased.

 

Thanks for you support.

Regards

  Hansi

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-06-20 11:30 PM . Last Modified: ‎2022-06-20 11:31 PM

In response to JanKarsten
0 Likes
5
2891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-20 11:30 PM . Last Modified: ‎2022-06-20 11:31 PM

Hello @JanKarsten 

 

As it is with bugs and development in general, it is a bit hard to be very exact here 🙂

 

In regard to the error, it is my understanding that this is a case of erroneous alarms and not something that can have implications on the actual "UPS" function. That being said, at the very least, you will have a log that becomes cluttered with these alarms. But as mentioned, this is my understanding and I do not have definite knowledge to back this up. With that in mind, I would advise downgrading.

 

In regard to the timeline on the next version of the firmware, again I am not able to give you anything definite.

But, as far as I know, the firmware has been developed and is currently going through the test cycles.

That would normally indicate that we are looking at weeks, instead of months, until release.

 

Best regards

Tonny 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JanKarsten
JanKarsten
Cadet

Posted: ‎2022-06-27 01:12 AM

In response to TonKei
0 Likes
0
2777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-27 01:12 AM

Hello @TonKei 

 

Thank you for the information.

 

I have downgraded the USVs and now the "error messages" are gone.

 

Everything looks fine at the moment.

 

Looking forward to the release of the fixed firmware.

 

Best regards,

Jan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LarryK
Lt. Commander LarryK
Lt. Commander

Posted: ‎2022-07-14 05:57 AM

In response to TonKei
0 Likes
3
2700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-14 05:57 AM

@TonKeican you please confirm whether the 2.2.1.1 firmware, released July 1 fixes this issue?

 

Thanks!

Larry

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Matt-B
Lieutenant JG Matt-B Lieutenant JG
Lieutenant JG

Posted: ‎2022-07-15 10:23 AM

In response to LarryK
1 Like
2
2657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-15 10:23 AM

Hi @LarryK,

 

Yes, v2.2.1.1 fixes the erroneous bypass event issue. Here's a link to the release notes for the SmartUPS app for the full list of updates: https://download.schneider-electric.com/files?p_Doc_Ref=SPD_CCON-SURELNOTE_EN&p_enDocType=User+guide...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KLJ
KLJ
Cadet

Posted: ‎2022-07-15 11:13 PM . Last Modified: ‎2022-07-15 11:14 PM

In response to Matt-B
0 Likes
1
2648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-15 11:13 PM . Last Modified: ‎2022-07-15 11:14 PM

Can confirm. After applying the new firmware the error messages UPS:In bypass in response to an internal hardware fault no longer happen.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Hansi98
Crewman Hansi98
Crewman

Posted: ‎2022-07-19 10:46 PM

In response to KLJ
0 Likes
0
2598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-19 10:46 PM

I can also confirm: After applying 2.2.1.1 there are no false bypass messages any more.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of