Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

AP9635CH no connectivity

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9635CH no connectivity
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:42 AM

0 Likes
5
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:42 AM

AP9635CH no connectivity

I've lost network connectivity to my Symmetra PX 250/500 about two days ago.  No changes were made either on the network or on the UPS, yet I am no longer able to ping the UPS or access the web console. Upon physical inspection of the UPS I found that the status light on the AP9635CH NMC is constantly flashing green and amber very rapidly.  Even after disconnecting the network cable from the card the status light remained the same. I've performed the following troubleshooting steps:

  • Pressed the reset button on the NMC for a few seconds and waited for it to reboot.
  • Removed and reseated the NMC.
  • "Hard" reset the NMC by pressing in the reset button for 20 seconds.  Confirmed the status light was flashing green while I pressed the reset button then let go once it began flashing amber.
  • Reloaded the firmware on theNMC using the following files:
    • apc_hw05_bootmon_108.bin
    • apc_hw05_aos_632.bin
    • apc_hw05_sypx_632.bin

Status light remains the same constantly flashing green and amber very rapidly.  Are there any additional steps I can take to attempt to resolve this?  Or this indication of a failed NMC?  Any help/suggestions would be greatly appreciated.

 

Thanks.

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

Hi David - sorry, was out on vacation. I will PM you a link to the newer firmware we have which I checked is okay to work with 4.29.11. Usually a field service rep is required to do these because there is often an NMC/UPS compatibility matrix but no worries for the 6.4.0 version I'll give you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:42 AM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:42 AM

Hi David,

Great troubleshooting steps so far. Have you tried connecting serially to the NMC through the console port?

When you reloaded the firmware, were you able to do that while the status LED was flashing amber/green rapidly? That would indicate the card is rebooting. But, if you formatted it like you said, this typically clears up most issues as reboot loops are often firmware issues or something hung up. It could also be that the NMC is having a problem communicating to the UPS. I've seen a reboot loop once so far be an NMC hardware problem.

Can you verify on the UPS display that the slot the NMC is in is still configured for Read/Write access? And does the display let you configure TCP/IP settings to the NMC? Can you see anything in the logs on the display?

Random question: you don't happen to have another UPS, not necessarily PX250/500, that we can install the AP9635 into to see if it exhibits the same behavior?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

Angela,

Thanks for your response.  I have not tried connecting serially to the NMC yet, at the moment I am trying to track down the cable required to do this.  Once I aquire one I will give it a shot.  To reload the firmware I used a USB flash drive.  I formatted the drive with FAT32 and loaded the necessary files.  I plugged in the USB flash drive to the top port of NMC and pressed the reset button.  The NMC rebooted and I could see the status light flash amber for several seconds and then green for about a minute.  It then appeared to do another reboot and that is where it went back to the rapid green/amber flashing. 

I checked the UPS console and confirmed the NMC is still configured for read/write access.  I am able to change tcp/ip settings.  All the logs show are entries whenever UPS loses communication to the NMC and once it restores, these are logged when I press the reset button on the card.  Unfortunately I do not have another UPS where I can test this NMC on.

 

Thanks.

 

-David

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

Hi David,

What firmware is on your UPS itself? It should be something like v4.X.X I think. I was just thinking there is a new sypx firmware out there we could try via the USB upgrade method. I don't have high confidence it will change anything but we need to make sure your UPS firmware is new enough to support the newer NMC firmware, assuming you wanted to give it a try. It is very strange it happened out of nowhere. 

I thought of one other thing too. To rule out any strange packets the NMC is having a hard time processing and is hanging it up, you could temporarily remove the network cable from the NMC and then press and release (or reseat) the NMC and see if it also behaves the same way with no network connection.

Beyond that, you may want to contact support. 3 phase support typically replaces everything (frown) so I imagine that is the resolution they'll give you as they are less knowledgeable than us here specific to the NMC. They are experts on the UPS though. I typically review all of the NMC RMA returns from NAM so if you send it back, it'd get to me eventually. Or I can send you a special return label to get it directly to me in a shorter amount of time and I can follow up with you with what I find, assuming what I said doesn't work and 3 phase support team agrees there is nothing else they know of that would cause this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

UPS firmware is 4.29.11.  If there is a newernmc firmware available I'd like to give it a shot, could you send me a link to the download location?

I have disconnected the cable and restarted the NMC.  However, no change in status.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

0 Likes
0
746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:42 AM . Last Modified: ‎2024-03-13 12:41 AM

Hi David - sorry, was out on vacation. I will PM you a link to the newer firmware we have which I checked is okay to work with 4.29.11. Usually a field service rep is required to do these because there is often an NMC/UPS compatibility matrix but no worries for the 6.4.0 version I'll give you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of