Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

AP9617 network management card able to obtain IP but unable to connect

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9617 network management card able to obtain IP but unable to connect
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

0 Likes
5
2635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

AP9617 network management card able to obtain IP but unable to connect

I have SMART-UPS 1500 XLM with network management card AP9617 installed. I connect this UPS to network and the UPS able to obtain IP address. I am able to PING the IP but unable to connect to UPS through telnet or web.

- I confirmed that there is no firewall rules preventing the access.
- If I use serial cable to configure the IP address, I am able to connect through telnet or web.
- I set the option 43 to = 0x01 0x04 0x31 0x41 0x50 0x43 but that doesn't help either.
- I reset the network management card and still unable to connect.

Any idea what might causing this issue?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

per buzz's statement: The new NMCs (AP9630, AP9631) have the cookie requirement disabled and will pull an IP via DHCP automatically.

please be advised this is only true for brand new cards shipping at AOS 5.1.1 and APP 5.1.1. if you ugprade from 5.0.x, where the default is Vendor Cookie: Enabled by default, the upgrade will maintain that setting and not turn the cookie off.

sounds like per buzz's suggestion, we need to either 1.) configure the vendor cookie option on your DHCP server or 2.) disable it inside of the NMC's console interface under the advanced options in the networking menu.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

I have SMART-UPS 1500 XLM with network management card AP9617 installed. I connect this UPS to network and the UPS able to obtain IP address. I am able to PING the IP but unable to connect to UPS through telnet or web.

- I confirmed that there is no firewall rules preventing the access.
- If I use serial cable to configure the IP address, I am able to connect through telnet or web.
- I set the option 43 to = 0x01 0x04 0x31 0x41 0x50 0x43 but that doesn't help either.
- I reset the network management card and still unable to connect.

Any idea what might causing this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

This part confuses me: "If I use serial cable to configure the IP address, I am able to connect through telnet or web."

So you ARE able to access the card via telnet/web some of the time?

When you connect using a serial cable, you should see "Stat: P+ N+ A+" above the control console, on the right hand side - can you verify these values?

Also while connected serially, if you go to 2 for network, 3 for ping utility, can you successfully ping addresses from the card?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

It shows "Stat: P+ N? A+" and when I try to access PING utility, it shows "network is not running."

I also see message "Network not started. Currently making a BOOTP request."

I believe the default for Boot Mode is DHCP & BOOTP? How come the UPS doesn't configure the IP, SM and GW properly?

Yes. If I use serial cable to configure IP, SM and GW and I am able to connect to UPS through telnet or web.

What I want to do is to have UPS able to obtain IP address then have the tech to login through web or telnet to configure the designated IP address for UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

The card can only receive an IP address via your DHCP if the correct cookie is setup under option 43 on your DHCP server. By default, the card requires this cookie setting so it doesn't pull an unauthorized IP. You can disable this requirement, also by logging in to the card serially. Otherwise you'll have to assign it an IP address yourself either via serial connection, ARP, or the IP utility that comes with the card (also a free download).

The new NMCs (AP9630, AP9631) have the cookie requirement disabled and will pull an IP via DHCP automatically.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

0 Likes
0
2635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:48 PM . Last Modified: ‎2024-03-14 01:17 AM

per buzz's statement: The new NMCs (AP9630, AP9631) have the cookie requirement disabled and will pull an IP via DHCP automatically.

please be advised this is only true for brand new cards shipping at AOS 5.1.1 and APP 5.1.1. if you ugprade from 5.0.x, where the default is Vendor Cookie: Enabled by default, the upgrade will maintain that setting and not turn the cookie off.

sounds like per buzz's suggestion, we need to either 1.) configure the vendor cookie option on your DHCP server or 2.) disable it inside of the NMC's console interface under the advanced options in the networking menu.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore