Does anyone have the schematics for the AP9617 Network Management Card? I'd like to build a small desktop box for configuring large quantities of these cards without having to use the large rack mount chassis. Has anyone attempted such a project? We deploy about 75 of these cards a year so not having a full UPS on my desk would be nice. I've seen such a box for managing larger building UPS units.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:46 PM . Last Modified: 2024-03-14 11:44 PM
Hi There,
APC cannot provide schematics of the AP9617 NMC but if a customer has made their own sort of drawing or outline, you're welcome to accept that at your own risk.
For mass configuration of cards...you could just configure one card with the settings you would like and push the card's config.ini file out to all the other cards via FTP. For assigning IPs you could set your cards back to defaults and erase TCP/IP settings and use our IP Configuration Wizard to "re-configure" each card with TCP/IP settings, or, again use the config.ini. Also, if you are doing mass firmware upgrades, you can utilize the iplist.txt file to push our firmware upgrades to any IP sets you wish.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.