AP9225 Outlets stuck in off mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9225 Outlets stuck in off mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

0 Likes
3
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

AP9225 Outlets stuck in off mode

I own several AP9225 MasterSwitch Plus units. They have been very reliable and I have never had any problems. However, I know have one unit in which the outlets are stuck in the off state and i cannot turn them back on. I have tried plugging them into another power source as well as pushing the manual button as well as the circuit breaker button with no luck. I have tried rebooting the unit as well and there are no errors in the error log file. I just can no longer turn them on.

I am assuming the PDU has finally failed and I am going to have to replace it. The green status light is solid on the front panel. It has a AP9617 card in it.

Any suggestions?

thanks

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • test
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

0 Likes
0
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

hmm agreed. it says communication established. what did you find for the firmware version?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

0 Likes
0
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

can you show us the event log from the network mangement card? i am wondering if the NMC lost communication to the PDU for some reason and cannot control the outlets anymore. any events from that would be helpful as well as the current firmware revision. i think that is listed under Help ->About

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

0 Likes
0
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

The event log has nothing in it but when the system boots and then tries to turn on the outlets and there are no errors. See below:

08/30/2011 07:29:12 MasterSwitch: Outlet 06 on device ap9225_2 delay turning ON.
08/30/2011 07:29:10 Management Card: Web User tdampier logged in from 10.0.0.6.
08/30/2011 07:29:02 MasterSwitch: Outlet 03 on device ap9225_2 turned OFF.
08/30/2011 07:28:56 MasterSwitch: Outlet 03 on device ap9225_2 delay turning ON.
08/30/2011 07:28:44 MasterSwitch: Outlet 07 on device ap9225_2 turned OFF.
08/30/2011 07:28:44 MasterSwitch: Outlet 06 on device ap9225_2 turned OFF.
08/30/2011 07:28:44 MasterSwitch: Outlet 05 on device ap9225_2 turned OFF.
08/30/2011 07:28:44 MasterSwitch: Outlet 04 on device ap9225_2 turned OFF.
08/30/2011 07:28:44 MasterSwitch: Outlet 03 on device ap9225_2 turned OFF.
08/30/2011 07:28:44 MasterSwitch: Outlet 02 on device ap9225_2 turned OFF.
08/30/2011 07:28:44 MasterSwitch: Communications established with device ap9225_2.
08/30/2011 07:28:44 MasterSwitch: Outlet 07 on device ap9225_2 delay turning ON.
08/30/2011 07:28:44 MasterSwitch: Outlet 06 on device ap9225_2 delay turning ON.
08/30/2011 07:28:44 MasterSwitch: Outlet 05 on device ap9225_2 delay turning ON.
08/30/2011 07:28:44 MasterSwitch: Outlet 04 on device ap9225_2 delay turning ON.
08/30/2011 07:28:44 MasterSwitch: Outlet 03 on device ap9225_2 delay turning ON.
08/30/2011 07:28:44 MasterSwitch: Outlet 02 on device ap9225_2 delay turning ON.
08/30/2011 07:28:22 Management Card: Warmstart.
08/30/2011 07:27:56 MasterSwitch: Outlet 04 on device ap9225_2 turned OFF.
08/30/2011 07:27:56 MasterSwitch: Outlet 03 on device ap9225_2 turned OFF.
08/30/2011 07:27:56 MasterSwitch: Outlet 02 on device ap9225_2 turned OFF.
08/30/2011 07:27:50 MasterSwitch: Outlet 08 on device ap9225_2 turned OFF.
08/30/2011 07:27:50 MasterSwitch: Outlet 07 on device ap9225_2 turned OFF.
08/30/2011 07:27:50 MasterSwitch: Outlet 06 on device ap9225_2 turned OFF.
08/30/2011 07:27:50 MasterSwitch: Outlet 01 on device ap9225_2 turned OFF.
08/30/2011 07:27:46 MasterSwitch: Outlet 08 on device ap9225_2 delay turning ON.
08/30/2011 07:27:46 MasterSwitch: Outlet 07 on device ap9225_2 delay turning ON.
08/30/2011 07:27:46 MasterSwitch: Outlet 06 on device ap9225_2 delay turning ON.
08/30/2011 07:27:46 MasterSwitch: Outlet 04 on device ap9225_2 delay turning ON.
08/30/2011 07:27:46 MasterSwitch: Outlet 03 on device ap9225_2 delay turning ON.
08/30/2011 07:27:46 MasterSwitch: Outlet 02 on device ap9225_2 delay turning ON.
08/30/2011 07:27:46 MasterSwitch: Outlet 01 on device ap9225_2 delay turning ON.
08/30/2011 07:27:40 MasterSwitch: Outlet 06 on device ap9225_2 turned OFF.
08/30/2011 07:27:40 MasterSwitch: Outlet 05 on device ap9225_2 turned OFF.
08/30/2011 07:27:40 MasterSwitch: Outlet 04 on device ap9225_2 turned OFF.
08/30/2011 07:27:34 MasterSwitch: Outlet 07 on device ap9225_2 turned OFF.
08/30/2011 07:27:34 MasterSwitch: Outlet 06 on device ap9225_2 delay turning ON.
08/30/2011 07:27:34 MasterSwitch: Outlet 05 on device ap9225_2 delay turning ON.
08/30/2011 07:27:34 MasterSwitch: Outlet 04 on device ap9225_2 delay turning ON.
08/30/2011 07:27:30 Management Card: Event Log cleared.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

0 Likes
0
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:10 AM . Last Modified: ‎2024-03-18 02:40 AM

hmm agreed. it says communication established. what did you find for the firmware version?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore