We have some PDU that we are powering via the subfloor. The PDU network Management module is upside down due to subfloor power.
I am aware of the keystroke to rotate the display.
But it appears that the module may be able to be unscrewed and rotated. Is this the case and if so is it APC supported? I don't want to void the warranty etc.
Thanks,
Neal
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:55 AM . Last Modified: 2024-03-18 01:06 AM
It is only intended for you to rotate the display 180º by holding down the key combination. The display is intended to be field replaceable in case of fault or problem and requires a full power down of the PDU to replace so that is why you see screws. It is not intended to be rotated physically.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:55 AM . Last Modified: 2024-03-18 01:06 AM
It is only intended for you to rotate the display 180º by holding down the key combination. The display is intended to be field replaceable in case of fault or problem and requires a full power down of the PDU to replace so that is why you see screws. It is not intended to be rotated physically.