AP8653 firmware update

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8653 firmware update
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
whoamigr
Crewman whoamigr
Crewman

Posted: β€Ž2024-08-20 05:04 AM

0 Likes
3
2325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-08-20 05:04 AM

AP8653 firmware update

Hi, I have a question. I have several AP8653 that I updated to the latest firmware, with some of them upgraded to version v7.1.4 and others individually to v3.1.1.4. All the PDUs are the same model AP8653 but have different NMC models, AP9538 and ON-1570. Can I push the same update to all PDUs, or does each NMC require its own specific version?

  • Tags:
  • AP8653
  • apc
  • english
  • firmware
  • pdu
  • rpdu
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: β€Ž2024-08-20 07:34 AM

0 Likes
0
2318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-08-20 07:34 AM

Your first task is to confirm what NMC is installed to each unit: NMC2, NMC3, etc

 

Next, confirm which NMC is subscribed to the APC SNS if at all. Knowing both above will guide you to which firmware is applicable to your specific environment.

 

The NMC2 is end of life and the latest firmware is v7.1.6. The NMC3 without the SNS Subscription you can use v7.1.6 firmware also. 

New APC NMC3 coming out of the factory come with 3.XX firmware and also have the option to subscribe to the Secure NMC System (SNS).

 

Lastly, to add even more confusion when the SNS was first launched the firmware started at v1.XX ~ 2.XX firmware which is now as of 2024 3.XX! πŸ€¦β€β™‚οΈ

 

NOTE: Once you have confirmed which firmware version applies to you. Ensure you have the APC FAQ as it relates to recovering the NMC should the firmware go sideways! 

Do (NOT) try to upgrade a NMC that is at a major level behind. 

IE: NMC 2 Increment from say v5.XX -> 6.XX - 7.XX. Any NMC 3 that is on the SNS firmware say 1.XX must be upgraded to 2.XX before you go to 3.XX.

 

Lastly, better have a hot spare available! 🀣

Reply

Link copied. Please paste this link to share this article on your social media post.

whoamigr
Crewman whoamigr
Crewman

Posted: β€Ž2024-08-25 10:54 PM

0 Likes
0
2231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-08-25 10:54 PM

Dear TekenThank you so much for your detailed response! Your explanation was very clear and easy to understand. I appreciate the guidance, and I'll make sure to follow your advice regarding the NMC models and firmware updates.

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

jeremyhu
jeremyhu
Cadet

Posted: β€Ž2025-01-19 01:05 AM

0 Likes
0
1688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-01-19 01:05 AM

Where do we actually find these incremental (and latest) firmware?  Searching SE's site for AP8653 firmware only results in apc_hw21_rpdu2g_2-5-0-6.nmc3.  As expected based on this post, this fails for my NMC2 units.  However, it also fails to deploy to my NMC3 units running rpdu2g v1.2.0.4.  Also, this doesn't seem to be the latest version as I have a newer unig with v3.0.0.5 ...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore