Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
AP7920B Loose Connections
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-1601:55 AM
AP7920B Loose Connections
Hi
We've purchased some AP7920B units.
All power cables into each socket feel loose. If they 'droop' downwards the power will be lost.
This is alleviated by using cable ties on the retention bracket to force the cable to remain in position but it is not ideal.
We are using LINDY brand IEC cables (C13 to C14).
I wanted to check if there are APC brand cables which provide a better connection, or any advice on specific cables to use for a more secure connection.
There are some latching APC cables provided for the AP8xxx series (yellow ones) but I can't see anything specific for the AP7xxx series.