I am trying to obtain power being used by devices connected on the AT4421 that I have. The Web GUI is showing 0 for the output power and I don't see a way to get it via SNMP. Is this a bug in
Tim
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:38 AM . Last Modified: 2024-03-18 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:38 AM . Last Modified: 2024-03-18 11:25 PM
And thanks for the OID info
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:37 AM . Last Modified: 2024-03-18 11:25 PM
Hi Timothy,
To clarify, are you saying the ATS shows 0 load connected, when there are in fact devices plugged in? Do you know roughly what the amperage should be showing based on the amount of devices plugged into the ATS? Does the ATS show any load on the front display?
The full OID tree for output status is under the atsStatusOutput folder: .1.3.6.1.4.1.318.1.1.8.5.4.3
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:37 AM . Last Modified: 2024-03-18 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:37 AM . Last Modified: 2024-03-18 11:25 PM
Hi
Yes, there were devices plugged in and the load showed as 0. I had reboot the interface card and it made no difference. Today we upgraded it to the latest version and now we have a valid load showing in the interface.
Tim
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:38 AM . Last Modified: 2024-03-18 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:38 AM . Last Modified: 2024-03-18 11:25 PM
And thanks for the OID info